A
alanl
I've just been to change an oven tonight, should have been a straight swap.
Large cooker isolator, fine, MCB at 32A, no RCD protection. Not brilliant, but OK for a like for like.
Isolate, remove oven, then find the old oven is plugged into a double socket, with the hob ignition in the other plug.
Hmm, this is not right, so, I check the new oven, and see if it is rated low enough for a 13A plug fitting. No way, maximum demand 3.5kW, and Installation instructions say must be on a DP fused connector.
So, I'm going to have to fit a FSU, well 2 actually, as the hob needs sorting too. Then, because I'm modifying the circuit, I'll have to give it RCBO protection (cable <50mm).
*This is getting complicated for what should have been a 20 minute job.
Firstly, with a 3.5kW rating, the fuse needs to be 15A to cope with max demand. I cant say I've ever seen a 15A fuse. Use a 13A?
Is my thinking correct in this - it must be done right as it is a rented property.
Ta
Alan.
I'm just an apprentice with no books on me. But can't u apply diversity?
You can't just put a 15a fuse on something that needs 13a without checking if you can add diversity otherwise I'm guessing a 20a DP switch??
There is no diversity, as it is only one item fed from one FSU.*
Full power is 15A according to the manual, in reality, it would likely be 13A anyway, just wondering if people put a 13A on these usually?
Shouldn't it be done right because you're a qualified Spark working to the Regs? :)
Of course, that's why I left it disconnected. It would have been a 5 minute job to fit a plug, but I have a conscience, and want to do it correctly. My initial idea was to fit a FSU, but I'll then be modifying the cirtcuit, so will need to fit an RCD. So a £40 bill has gone up to £75.
Today I approached Neff because a customer had asked me to wire up a cooker (2.8Kw) he had acquired, without a manual.
The Neff reply is as follows:
"Dear Mr x,
Thank you for your email.
The I E E Wiring Regulations, 17[SUP]th[/SUP] Edition, (regulation 433.1.5) states that cookers, ovens and hobs with a rated power exceeding 2 kW should be connected to their own dedicated radial circuit."
So I got out my regs and can't see this in 433.1.5
Any comments?
what size cable is on the cooker, if any?
It's on 6mm, so no problem with current carrying capacity. As it happens, I have a 20A RCBO spare, so that can be fitted, but I thought I'd see others views on how this should be done - the Landlord is not going to be happy, as the cost of fitting has doubled, and i'd just like confirmation that I'm doing it correctly.
Ta
Alan.
"Dear Mr x,
Any comments?
I've heard of this. Although "over 3KW" Sounds familiar. Not sure why
I personally would ask the client to change the oven to a less powerful model, only encountered this situation once mind and to run in a new circuit would have been a nightmare.
The only place I can find in the BGB is app.15 reg 434.1.103 : connect cookers, ovens & hobs with a rated power exceeding 2kW on their own dedicated radial circuit.
Cant see you having a problem just putting it on a plugtop TBH
Regards gram
Sent from my iPhone using Tapatalk
but if you have a cooker isolator on a dedicated circuit, use that with a cooker outlet plate.
I had exactly the same thing. Asked to wire up a cooker like for like. Original cooker on a 13a fcu spurred off kitchen ring. Looked at new cooker like you said its 3.5KW. Could not find the rating for the old cooker but obviously new is 15 + amps (possibly)
Problem is the place is a flat immaculately decorated no way could I run a new feed (cost single mum etc...) I am aware (or believe) that anything over 2KW should have its own dedicated circuit so I explained the situation to customer and connected the new cooker into the 13A RCD FCU (no RCD protection previously) as I thought I could apply diversity (first 10 amps then a third = 12A ish) as it would not all be running at the same time. I put this on the MWC and got customer to counter sign. this was over two weeks ago and no problems.
I know its not the best practice but the worst case scenario would be the fuse go? I have been trading for just over a year now and I find things like this crop up all the time, I can't just walk away principles get too expensive otherwise.
What app 15 says regarding connecting cookers etc over 2kW to their own dedicated circuit is not a regulation it is a method of ensuring the requirements of reg 433.1.5 can be met. What is important however is reg 433.1 which states "every circuit shall be designed so that a small overload of a long duration is unlikely to occur". I would suggest that putting a 15A cooker on a 13A fuse contravenes this.
Yes, thinking about it the oven would get up to temperature, probably pulling 15A then the stat would switch it on and off as required so the overload wouldn't be a long duration.
There is no way 15A would blow a 13A fuse so feeding the oven via a plug top is OK then??
If that oven ever see's 15A it'll be a miracle!!! This is almost becoming a daily occurance on the Forum, of where sparks can't get it round their heads that these ovens are rated at ''connected load'' and that connected load is unlikely ever to be seen, because there are heating/cooking elements that cannot be utilised at the same time!!!
Some of the posts on this thread, clearly indicates that there is a lack of understanding whenever they come up against cookers, ovens, and split hob and oven set-ups. They still look at the total KW rating and start panicking, and up goes the size of the cable and the MCB rating, all to the cost of their customers.
This oven can go on an FCU with a 13A fuse, ....end of!!!
Reply to Oven on FCU? But what size fuse? in the Australia area at ElectriciansForums.net
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
4K