Hi guys,

Some of PV installators told me that they want 4KW inverters with the max out put of less than 16A/phase. But G83 defines that is the reuqirement to systems less than 3.7kw. For 4kw, the safty should be G59. Could anyone tell me why some installators hope to get 4KW under 16A?

Thanks in advance.

LQY
 
Google for instance,

Aurora Power One PVI-3.6-OUTD 16A limited

or

SMA Sunny Boy 3800 16a limited

or

I think the G83 SMA4000TL is also limited to 3680, not sure

Just a some that I have used recently, like them both
 
Last edited:
In response to the OP, the reason people try for 4kW is that is where the break in the FIT tariff is. Everything up to and including 4kW gets the highest rate. Therefore if you can install 4kW rather than 3.68kW and keep it on G83 you maximise your return on investment. Whilst the G83 standard is designed around 16A per phase, the G83 tests on inverters do not specify keeping the current below 16A. So it is possible for an inverter to be working in the G83 regime (in terms of under/over voltage and under/over frequency cut-offs) whilst actually working above 16A. In the past many DNOs were relaxed about this, but as more solar pv and other distributed generation is being deployed they realise they are making a rod for their own back offering the flexibility and so are now tightening up and keeping people within the 16A (3.68kW) limit. Going to G59 rather than G83 means prior negotiation with the DNO, potentially some network upgrade costs and often a more difficult design because for example the over-voltage limit is tighter (253V rather than 264V).
Regards
Bruce
 

Reply to Question about G83 requirement of 16A each phase in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi all I had my PV/Battery setup installed in May and since then all my excess PV is just fed back to the grid for free. When I initially tried...
Replies
1
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock