Hi

I am trying to fill in the Condition Report Inspection Schedule for Domestic Premiss with up to 100 A Supply. I have a question regarding filling in the Section (5.10) That states Concealed cables installed in prescribed zones. My installation reference method is B and there is no way of finding how deep the cables are or or if they in prescribed zones but they are RCD protected. What is the extent and limitation in this case? Is it 100% limitation or 50%? Or is it N/A? I know that i have to mention it in section D (extent and limitation) of the report.

Many Thanks
 
I promise you it is the last question I ask for now and I ll deal with the rest myself.

Many thanks
 
are you sure its ref method B ?
clipped direct to wall is ref C

anyways , you dont have to write anything in the report for cables in walls & floors that you cant see , its already noted on the first page of the eicr under limitations - have a look.

the inspection sample rate of 30% 50% or whatever , is for accessories such as lights , sockets etc , its not for cables as most houses only have about 2% of visible cable on show.


in the section " cables in prescribed / safe zones " , just write N/V ( not verified )
 
are you sure its ref method B ?
clipped direct to wall is ref C

anyways , you dont have to write anything in the report for cables in walls & floors that you cant see , its already noted on the first page of the eicr under limitations - have a look.

the inspection sample rate of 30% 50% or whatever , is for accessories such as lights , sockets etc , its not for cables as most houses only have about 2% of visible cable on show.


in the section " cables in prescribed / safe zones " , just write N/V ( not verified )

Glad you clarified that for the OP biff, have an awful vision of him smashing the gaff to bits for inspection lol.
 
it's OK mark. he's not lofty.
 
  • Like
Reactions: 1 person
I am sure the reference method for erection is B as the cables are concealed in the walls and protected by 30 ma RCD. So I ll take your advise as N/V. And there is no further investigation required?

Many Thanks.
 
Last edited by a moderator:
I am sure the reference method for erection is B as the cables are concealed in the walls and protected by 30 ma RCD. So I ll take your advise as N/V. And there is no further investigation required?

Many Thanks.

Ohh ye of little faith, Biff gave you the answer, and you are doubting it...naughty boy.

Here is a recently posted article on reference methods that YOU will find useful http://www.electriciansforums.net/i...lations/70017-reference-method-explained.html
 
  • Like
Reactions: 1 person
Sorry to bother you again!

I still have a problem with this question. I am not sure whether this would require Further Investigation or not?

Sorry again biff n many thanks.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Question regarding filling in extent and limitation. Please help.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
nazoom,
Last reply from
markc123,
Replies
11
Views
2,884

Advert