I normally find that RCDs pass both tests, however there are a few that fail (which is worrying since if they can fail from new when might they fail in use?).
I have just had a 30mA RCD test OK on a new install and then when it was actually under use it failed to reset even when the fault was clear.
I find that the trip times are much closer to the regulations limits with the modern RCDs with their electronic control, whereas I find older RCDs trip much faster but at the same time for both 1x and 5x.
If a replacement device fails on testing then I would suspect that there was a problem with the attached circuits and ensure that there was only the incomer attached and test then, if it still fails then it was two faulty units in sequence.
I have just had a 30mA RCD test OK on a new install and then when it was actually under use it failed to reset even when the fault was clear.
I find that the trip times are much closer to the regulations limits with the modern RCDs with their electronic control, whereas I find older RCDs trip much faster but at the same time for both 1x and 5x.
If a replacement device fails on testing then I would suspect that there was a problem with the attached circuits and ensure that there was only the incomer attached and test then, if it still fails then it was two faulty units in sequence.