Hi my daughters rented home set on fire. The consumer unit was making a massive popping noise which shook the house. The boiler is in the same cupboard under the stairs and is 2 inches away from consumer. Is that normal practise? Plus a chappie came to fit a smart meter and told my daughter that there was a live wire dangling down so he taped it up.
 
I assume the landlord hasn't had an Electrical Installation Condition Report carried out. It will soon be a legal requirement every five years minimum. Information for Landlords & Responsibilities | Electrical Safety First - https://www.----------------------------/guidance/advice-for-you/landlords/
It is the landlord's responsibility to ensure the flat is safe to rent out including the safety of the electrical installation.
Should be a minimum 150mm between gas pipes and a fuse board I believe, unless there is a panel of insulating material.

Excerpt from BS6891:2015:

8.4.2 Separation of pipework from electrical services
8.4.2.1 Where installation pipework is not separated from electrical equipment
or cables by an insulating enclosure, dividing barrier, trunking or conduit, it shall
be spaced as follows:
a) at least 150 mm away from electricity supply equipment, such as metering
equipment, main service cut-outs or supplier (main) isolation switches, and
distribution boards or consumer units; or
b) at least 25 mm away from electrical switches, sockets and electricity supply
and distribution cables.
8.4.2.2 The installation pipework shall not be positioned in a manner that
prevents the operation of any electrical accessory, i.e. a switch or socket outlet.
NOTE Where these spacing requirements are impracticable the pipework should
either be sheathed with an electrical insulating material rated at 230 V ac or more,
or a panel of electrical insulating material should be interposed.

How bad is the fire? Have the insurance company been around?
 
Hi, thank you Derek. Also in February a chappie came to fit a smart meter he found a live wire dangling down so he taped it up. He said if she had touched it she could have died. Could that have had something to do with it?
 
Hi, thank you Derek. Also in February a chappie came to fit a smart meter he found a live wire dangling down so he taped it up. He said if she had touched it she could have died. Could that have had something to do with it?
I would say they are related as that sort of thing is a C1 fault - immediate danger - the highest risk in an inspection report, and it implies the system was basically unsafe and has not had any recent inspection by anyone competent!
 
  • Funny
Reactions: Mtgmmd
I'd be questioning why the meter installer didn't report this as near miss to his company and isolate the supply until it was made safe. A bit of tape is not safe isolation. At least this would have triggered the landlord to make the installation safe.
 
  • Like
Reactions: derek and ruston
Goes to show how much of an electrician the meter fitter was.

Any exposed live cable is a serious infringement of health and safety. The meter fitter hasn’t left it any safer, just brought it to the occupants attention.

Get onto the landlord and get him to sort it.
Lockdown or not, this is an urgent, and essential repair.
 
  • Like
Reactions: pc1966
That begs the question "how much of an electrician was the meter fitter" was the wire live or just a brown cable, how did he isolate it to wrap it in tape? Be interested to know the source of the fire? Consumer unit making a popping noise that shook the whole house? Boiler in the same cupboard, Gas leak? Notwithstanding all the above the landlord needs to sort this prior to your daughter returning to her accommodation. One assumes the insurance company have been informed, if so make sure your daughter claims for any consequential losses, including temporary accommodation even if she was staying with you.
 
  • Agree
Reactions: Mtgmmd
Can you post a photograph of the consumer unit? (remove/obscure any obvious personal identification of course)

As Mike says, any loud noise could be from the boiler but I presume there is good reason to identify the CU as the problem (signs of smoke/melting/etc)?
 
  • Like
Reactions: DPG
For a consumer unit fault to shake the house, there must have been one hell of a mess. Have you any photos of what happened?
 
Not very helpful, but very profound. :rolleyes:
 
  • Funny
Reactions: Risteard
If I were the tenant my --- would be straight on the phone to landlord and if they fobbed it off then I'd get a spark in and have the bill sent to landlord, I'd be inclined to make the metering company aware too, possibly even local authority also
 
This is always assuming that the fault that shook the house was electrical? The Boiler was in the same cupboard! mind you we have not established if the boiler was gas, oil or electric.
 
Goes to show how much of an electrician the meter fitter was.

Any exposed live cable is a serious infringement of health and safety. The meter fitter hasn’t left it any safer, just brought it to the occupants attention.

Get onto the landlord and get him to sort it.
Lockdown or not, this is an urgent, and essential repair.
Thank you. The house finished up being on fire. So my now daughter has to be evacuated. New boiler, consumer unit and a full paint job through the whole house
 
Any photos? Do you know what actually caused the fire?
 
  • Agree
Reactions: telectrix
Thank you. The house finished up being on fire. So my now daughter has to be evacuated. New boiler, consumer unit and a full paint job through the whole house

What have the fire brigade identified the cause of the fire to be?
 
Fuel, oxygen and a sufficient heat source :p
[automerge]1589051730[/automerge]
As someone who does fire risk assessments I find fire fascinating probably a childhood arson thing, not an extreme childhood issue but understanding it is rudimentary. Just look up fire and the candle effect, explains nearly all fire origins.
 
Last edited:
As someone who does fire risk assessments I find fire fascinating probably a childhood arson thing, not an extreme childhood issue but understanding it is rudimentary. Just look up fire and the candle effect, explains nearly all fire origins.

I find fire fascinating too, and fun, and one of my many jobs is all about starting fires (in the right places)

It always amazes me how many people don't understand such a rudimentary thing, the number of times we end up stepping in to help light the bonfire at the events we do in November is ridiculous.
 
  • Agree
Reactions: westward10
Thank you. The house finished up being on fire. So my now daughter has to be evacuated. New boiler, consumer unit and a full paint job through the whole house
Good to hear the outcome has been satisfactory as the single most important thing is your daughter is fine!

Folk here always want to find out what depend so we, as far as humanly possible, can make sure it does not happen again on any setup we have dealings with.
 
  • Like
Reactions: DPG
I never tire of telling people that wood does not burn it is the indirect action of heat and gas separation creating combustion, I am the life and soul of any party :tearsofjoy:
 
  • Funny
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Should a consumer unit be fitted 2 inches from a boiler?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
Mtgmmd,
Last reply from
Mtgmmd,
Replies
26
Views
3,193

Advert