we have been asked to quote for a 3.80kw pv system on a roof which is 60m away from the main distribution board, there is a sub main in the building where they want the pv system installed which has a few spare way on it, this submain is fed by a 16mm 3 core swa,

do i need to take the pv supply all the way back to house or can i install it to the sub main, would that work,

please help
 
I think you'll need to look at a new cable run
reccommended volt drop for AC side of pv is 1%
regs recognise this may be costly and will permit within BS 7671 limits.
In theory the submain will have to carry the extra 3.8kw
and should be sized appropriately anyway and comply with the 1% Vd .
on the PV jobs we've done with the longest run being 65mtrs it was easier to install the cable than to try and work out the load/diversity/also PIR of circuits on the submains, especially as this takes time and you 're just quoting for work, or the submains in question were too small for they're intended loads ,even with diversity applied!
 
thanks for that reply i think i will be better to run a new cable i then. the only thing is at the main consumer board there is no spare ways, so can i install a new small consumer board next to the main consumer board, will that work
 
Ther was a very similar question on the IET forum over the weekend and the answer from someone whose professional job is designing all sorts of installations was that in principle it is OK to connect at the end of a sub-main. The PV needs its own circuit after the sub-DB of course.
IET Forums - Connecting Solar PV
Regards
Bruce
 

Reply to sub main 60m away from house, pv system to get installed on sub main roof in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
839
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
795
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock