Thanks needasparks.
Just been on to the doncaster website as i was unsure of the csa of the cpc of the 10mm T&E and as it comes out at 4mm. My plan will be to running an additional 6mm cpc.



Edit
Sorry for the late response but i could not reply posts till today
 
Last edited by a moderator:
if your running trunking why don't you wire everything in singles and use MCB's?
if there is a suspended ceiling why don't you use cable tray above the ceiling?
 
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.
 
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.

Save your T&E for another job and use singles on this installation. Your already having to supply a separate single CPC conductor, so bite the bullet and do things properly by using the right installation cable....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Sub main board question
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
maluka,
Last reply from
Engineer54,
Replies
19
Views
3,780

Advert

Back
Top