been working on site today - came across someones bad calculations - there is 6mm swa in a ducting underground and it only comes out of the ducting at one end! i managed to dig down to the ducting and found the other end buried underground.
So what is the best way of connecting two pieces of swa in a ducting?? resin joints? or connectors in a connector box?
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
pull a new cable in. saves grief later.
 

Dave OCD

-
Mentor
Arms
Esteemed
If the join has to be underground I'd say a proper resin filled joint is by far the best way, any type of enclosure if buried will cause problems sooner or later.
 

Charlie_

-
Arms
Instead of digging it up and jointing it on the ground you could have jointed it at the other end and pulled the slack down through the duct
 

NDG Elecs

-
Arms
Esteemed
My maths are really rubbish too. I watch Rachel Riley religiously but my sums still don't add up!!
 