First time i have worked with steel conduit as a cpc and wondering how to get a decent R2 test.

The back boxes are showing signs of corrosion and so is the conduit where it is exposed so would like to test to see if i'll need to add a cpc to the circuits.

I have a kewtech 65dl tester and access to a wander lead.

The client ideally wants all the back boxes changed over and metal flat plate sockets added so want to make sure the cpc protection is there.

The previous owners wiring is a nightmare. There was an earth stolen off the bonding to supply two spur sockets and sockets spurred in all directions in trunking
 
get your mft with 1 lead clipped on the MET, other lead onto wander lead. null leads. then take end of wander lead to each accessory. record each resistance.
 
  • Like
Reactions: Wilko
If its showing signs off corrosion is it wise to use it as a CPC even if you do get an acceptable reading?
 
Thanks guys.

Thats what i was wondering Lee, even if i change all the back boxes over to new ones there will still be corrosion on exposed parts of the conduit. Someone suggested Galvanising Spray might work but i'm not sure on that.

The test certificate from 2 years ago has acceptable readings on it, but I've uncovered 6 sockets that were hidden behind the old kitchen that aren't very healthy looking
 
  • Like
Reactions: Leesparkykent
Testing will only give you your answer. Depends if the corrosion is only on the surface.. you'll be ok. I stripped out galv uni this week that was corroded by acid, you wouldn't have got much of a reading from that
 
Get hold of a ductor tester, the 100A test current will identify any poor connections!
 
  • Like
Reactions: seltechpc
You can, of course, get out there with a couple of pairs of pump pliers and conduit spanner to physically check the conduit joints. - that is, the ones that are visible. That should give some indication of the quality of installation
 
If the conduit is corroded then it may no longer be suitable as an earthed metallic enclosure for single insulated cables.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Testing steel conduit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
ElSteenio,
Last reply from
davesparks,
Replies
8
Views
1,942

Advert