... well, a clamp is a ring ... therefore ... still way too small!

Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.
 
Last edited:
Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!
k1/k2 * S
k1 for copper is 143, k2 for steel is 51, S= 3.63mm²
so S for steel needs to be (143/51)*3.63 = 10mm², you only have 5mm² (approx)

Hope they actually do something about it.
 
Thanks Richard..

Of course!! I'd only just been looking at table 54.2!

I've never used the K factor for steel before.. and there was me trying to be all clever with conductivity ratios.. just looking foolish really! :smile5:
 
Last edited:
Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.

There shouldn't be a cpc connected to the clamp at all!
 
I had a loose TN-S clamp on a CU change the other day - so I got the DNO out and they said it was fine,
different rules for them and us I suppose!
 

Reply to TN-S with a BS951 clamp and black tar covering supply cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just completed an EICR. The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this...
Replies
7
Views
3K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
I have just carried out an EICR at an old property and found this issue with the main earthing conductor. It has a TN-S system but the earthing...
Replies
32
Views
5K
Hi all. I'm currently training as an electrician so would like your views on this for clarity and if I need to get someone in? I have just moved...
Replies
9
Views
2K
Hi, Can I ask some advice on what to bury please? This is the the front of my house in plan view. House at the bottom. Porch at the bottom left...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock