... well, a clamp is a ring ... therefore ... still way too small!
Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.