- Dec 18, 2011
- 5,379
- 6,732
- 405,788
- If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
- United Kingdom
- What type of forum member are you?
- Practising Electrician (Qualified - Domestic or Commercial etc)
... well, a clamp is a ring ... therefore ... still way too small!
Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.