I recently came across an installation, very rough in practically all areas, however one thing caught my eye.

The TNS earthing arrangement was via a BS951 clamp onto the armour of the incoming supply cable. This wasn't a lead supply cable (as I have seen before with BS951 clamps) it was SWA with a section of the sheath cut and a clamp applied to the armour wires.

Now I am wondering if this is a DIY TNS as it is an old terraced house and a number of similar properties in the local area are TT earthing arrangement.

I am well aware that the incoming cable is the DNO property and if they see fit to supply an earth like this then so be it but it looks dog rough. What would your thoughts be?
20150618_123851_zpskz081deh.jpg
 
This is the thing it was a flying visit to do a recce on behalf of an estate agent. The tenant has made a complaint to the local building control/housing regulation regarding a number of issues and the building inspector cited electrical safety as one point.

I will ultimately be carrying out an EICR at the property but wanted some opinions on it before the time comes.
 
Does look rough. I think your best bet is to spend some time fully investigating it see what you come up with. Where is the CU?
 
  • Like
Reactions: 1 person
my first job would be a Ze to verify that the SWA armour was, in fact, earthed.
 
  • Like
Reactions: 4 people
Does look rough. I think your best bet is to spend some time fully investigating it see what you come up with. Where is the CU?

CU (old wylex rewireable) is just to the right out of the picture. No main bonding whatsoever, only 2 circuits for whole of house (lights and sockets), big gaping hole in front of cover....

It's not looking good!
 
I have no intention of doing anything other than listening to uncle Tel, I'm currently writing the estate agent a rather long winded email explaining why an EICR must be carried out without delay.

Do get rather sick of trying to explain to people (specifically tight a*sed landlords) why their installation is so unsafe while they try and tell me it has worked fine for years
 
  • Like
Reactions: 1 person
That's not a BS951 clamp, to comply with bs951 there must be a seperate terminal screw for the cable to connect to.
 
That's not a BS951 clamp, to comply with bs951 there must be a seperate terminal screw for the cable to connect to.

it's quite old, so it could be a BS CMLI,
 
  • Like
Reactions: 2 people
CMLI ........ Roman numerals for 951. Hehehe.
 
  • Like
Reactions: 6 people
my first job would be a Ze to verify that the SWA armour was, in fact, earthed.

If it is a row of properties,and the details of supply/earthing are not known,i would have a quick search of the route of your incomer/earth,BEFORE disconnecting,for your Ze. :yesnod:
 
  • Like
Reactions: 1 person
Why don't you ask the DNO to have a look, and see what they say about?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West Yorkshire

Thread Information

Title
BS951 clamp onto incoming supply SWA cable - DIY TNS?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
ray-bentos,
Last reply from
Midwest,
Replies
14
Views
6,784

Advert