Thanks for posting the update with the busted main switch. I'm still not clear on how this has caused a 20A MCB to trip quickly however, if I recall an earlier post correctly (?) .
 
  • Like
Reactions: DPG
Blimey, what's happened to this thread ??!!
 
  • Like
Reactions: Dave OCD and DPG
5pm !!
that's the time the annual christmas arm wrestling competition starts.
Have a good one !
 
  • Funny
Reactions: DPG
This will be my last post on this

First time we were called to fault with storage heater there was a live to earth fault on the existing cable fed from E7 consumer unit on a 16 amp 60898 MCB I’m not sure what the installation resistance was I didn’t go

Deakon ran a new 2.5 cable to heater that then worked for 4 day before tripping the 16 amp 60898 MCB.

Then we had the callback the next day and the day after we then installed a new 2.55kw heater
And put it on same MCB

Still tripped I went back as you know was getting voltage drop top of main switch constant 230v bottom ov main switch fluchuating between 210v and 235v ( there was a very low bussing Sond coming from main switch ) clamp meter going up and down 13amp to 16amps

Voltage did not fluctuate until 4th new storage heater was energised the new one (dint know why this is a mistery to me as much as you)

MCB did not trip when I was there for 30 min before E7 when’s of at 7pm when main switch changed

Worked last night we rang customer this morning and storage heater nice and warm

It’s not something I would believe myself but I was there and that’s what was happening

I hate ELECTRICS LOL

Merry Xmas every one
 
This will be my last post on this


Voltage did not fluctuate until 4th new storage heater was energised the new one (dint know why this is a mistery to me as much as you)

MCB did not trip when I was there for 30 min before E7 when’s of at 7pm when main switch changed

Worked last night we rang customer this morning and storage heater nice and warm

It’s not something I would believe myself but I was there and that’s what was happening

I hate ELECTRICS LOL

Merry Xmas every one
Well, fault proven or not, if everything works and tests OK, they should have a warm and safe Christmas.
Same to you. Enjoy!
 
5pm !!
that's the time the annual christmas arm wrestling competition starts.
Have a good one !
Well, fault proven or not, if everything works and tests OK, they should have a warm and safe Christmas.
Same to you. Enjoy!

just finished a callout to one of the less affluent areas of the city, their neighbour had their door kicked in and all the presents nicked, could be worse!
 
a) Dissapointed..No answerer to Marconi Post 187 Item-(d)
b) (reminded of previous Xmas break-ins "Tower block hell"- .......Cheers " El -sp " -I'm NOT travelling this year)
c) still sensing a non-resistive aspect (-Half facts-/vagueness)
-- Have Booze so will enjoy Xmas--
( Now suffering last Post disease--echolalai-varaint-B)
 
  • Optimistic
Reactions: 1 person
This thread has totally gone off subject, closing it down, you people need to open a thread on your xmas jollies and stop taking other threads off subject ...ps Merry Xmas
 
  • Like
Reactions: static zap

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
216

Advert

Thread statistics

Created
Steve Poulton,
Last reply from
Darkwood,
Replies
216
Views
36,660

Advert