N

Noob2013

Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.

Yes lets rip it all out and start from a fresh.. and then also get rid of the 100mA time delay RCD's from them old installs lol
 
Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
Hi Noob,

A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.

Also, if you don't already have it, get yourself access to the trainees forum.
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.
cobblers. this was most likely to regs. when installed. there's no requirement to bring it up to current regs. although any work done on the installation must comply to 17th.
 
cobblers. this was most likely to regs. when installed. there's no requirement to bring it up to current regs. although any work done on the installation must comply to 17th.

"most likely"

good enough for you. Not good enough for me.

As soon as he disconnects the tails to the existing he must be happy with the current installation before he reconnects it.

Just my opinion.
 
"most likely"

good enough for you. Not good enough for me.

As soon as he disconnects the tails to the existing he must be happy with the current installation before he reconnects it.

Just my opinion.

as long as it's safe for continued use. the fact that it was installed to a previous version of the regs. is no reason to condemn it. that's like condemning a 1990's car because it doesn't have abs or airbags.
 
Hi Noob,

A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.

Also, if you don't already have it, get yourself access to the trainees forum.

Can't we have an "Apprentice" badges Mods?
 
as long as it's safe for continued use. the fact that it was installed to a previous version of the regs. is no reason to condemn it. that's like condemning a 1990's car because it doesn't have abs or airbags.

Not condem but advise and make sure it is on the cert if the home owner does not want it.
 
Should this question not be on the Screwfix forum ?

You would use a MCB. But do you know why ?
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.

If I'm wrong, could you please explain?

Much appreciated
 
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.



If I'm wrong, could you please explain?

Much appreciated

ideally, you'd upgrade the board to give circuit division between 2 RCDs or, better still, RCBOs. but you can only do as much as the customer is prepared to pay. in this case, a MCB for the new circuit is the most cost effective solution.
 
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.

If I'm wrong, could you please explain?

Much appreciated

Your thinking along the correct lines. We're guessing to some degree as we don't know all the details but it seems ok.....if operation is satisfactory
 
Can you tell bt the front on an RCD if it is time delayed??

Yes it would be an S type RCD. Also, I can't see on here what rating (ma) the Main Switch RCD is. If it is 30ma then a RCBO (30ma) in series would be rather pointless. If it was a 100ma then it may be required dependant on circuit.
 
It will have a 'S' in a square.

But it if this is installed this will not give your circuit appropriate RCD protection.

whole DB change is what I would recommend.
Thank you.

So if the customer would not pay for that, and it was a time delayed rccb, could a new circuit not have an rcbo so it is protected?
 
Thank you.

So if the customer would not pay for that, and it was a time delayed rccb, could a new circuit not have an rcbo so it is protected?

Yes you will need to RCBO it. If the main is time delayed you will achieve the required discrimination between the RCBO & the RCCB.
 
Your crystal ball is obviously working better than mine! I can't quite see what the earthing system is or what rating that up front RCD is.

I am going on the info I have. As in my signature. Everything I say the installer should be happy within their own mind that it is correct.
 
As I posted before, It may be a 30ma RCD upfront already, he has not stated rating.

I know but we were specifically talking about if the RCCB is time delayed. In this case it would not give his new circuit the required protection so a 30mA non time delayed RCBO will be required.
 
Yes Noob you should not have 2 of the same mA RCDs in line, unless your RCCB is 100mA & time delayed.
As you have not given a mA for the RCCB which would normally be on the front, are you mistaking it for a ELCB?
You may need to take a pic of it so members can check.
 
Yes you will need to RCBO it. If the main is time delayed you will achieve the required discrimination between the RCBO & the RCCB.

From the description , and without looking at it !
I would say that the installation is likely to be TT , hence the up front rcd ( probably an 100mA S type ) so why or how could it possibly be failing any regs if the new circuit was to be just installed on a new rcbo ( even then if needed ? ) , instead of a whole new board !?
 

Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
491
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
300

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock