I like NYY-J much easier than swa but the chances of getting the length you require instead of a drum is remote whereas swa you can often get a cut length.
I've never used NYY-J cable, interesting. Does it come up to BS standard for a general installation, lights, sockets, etc?
I come across quite a bit of SY cable supplying 3 phase machines and external air con systems. I thought it was a bit of quick way of going about things, especially when not glanded correctly, as is usually the case....and have used it for feeding from panels or control units.
Is there not an argument for all the Y's being regarded as control rather than supply cables?
 
  • Like
Reactions: Adam W
These cables are nothing like YY, CY or SY. They are similar or the same essentially as High Tuff cables and comply to IEC60502 which is referred to in BS7671.
 
  • Like
Reactions: ipf
I'd never even heard of this "NYY-J" before today. It sounds like the old "pre-wired conduit" that was around before my time.
I don't see that it has any benefit over any other existing wiring system, such as flex in conduit. It sounds to me like an answer to a question which nobody has asked.
 
Nothing like pre-wired conduit or flex contained in conduit. It has low mechanical properties but most cables do but has good resistance from solar damage.
 
You're still not selling it to me - what can NNYJ cable do that SWA or black PVC conduit can't and how do you terminate this new cable?
So it's got good solar resistance (like black PVC conduit, SWA, even steel conduit); if you've only got a short run to go outside, what do you do with the thick sheathing on the rest of the run?
 
Not trying to sell it to anyone.
 
  • Agree
Reactions: ipf
H07RN is my go to cable for wiring machines
 
You're still not selling it to me - what can NNYJ cable do that SWA or black PVC conduit can't and how do you terminate this new cable?
So it's got good solar resistance (like black PVC conduit, SWA, even steel conduit); if you've only got a short run to go outside, what do you do with the thick sheathing on the rest of the run?
Pros and cons all round. Depends on the situation, really.
 
I like NYY-J much easier than swa but the chances of getting the length you require instead of a drum is remote whereas swa you can often get a cut length.
Hi-Tuff isn't uncommon here so cut lengths are often available.
 
Pros and cons all round. Depends on the situation, really.
There are pros and cons to each cable type, which aids in their selection, but I don't see where this NYY-J could be useful to me where nothing else exists that does it better.
 
SY cable manufacturers now state "SY control cables are not suitable for fixed wiring applications requiring compliance with the requirements set out in BS7671."
 
SY cable manufacturers now state "SY control cables are not suitable for fixed wiring applications requiring compliance with the requirements set out in BS7671."
"

That message clearly isn't understood ..... I've seen it being used for outdoor installations around and about
 
"

That message clearly isn't understood ..... I've seen it being used for outdoor installations around and about
As have I Murdoch used it a lot for the interlinking of indoor and outdoor A/C units, the A/C companies sometimes depending on which manufacturer you use, recomendusing it, so there is obviously some confusion, stopped using it when one of the brighter Lads in my unit pointed out the point that SY doesn't comply with BS 7671.
 
That message clearly isn't understood ..... I've seen it being used for outdoor installations around and about

It is only a recent change. We used to use SY for wiring up some equipment.
 
As have I Murdoch used it a lot for the interlinking of indoor and outdoor A/C units, the A/C companies sometimes depending on which manufacturer you use, recomendusing it, so there is obviously some confusion, stopped using it when one of the brighter Lads in my unit pointed out the point that SY doesn't comply with BS 7671.

I wasn't referring to fixing AC units... Garden lights...
 
^^

The last time I looked at the spec its range was -5 upwards, so unsuitable for outdoor usage surely
 
^^

The last time I looked at the spec its range was -5 upwards, so unsuitable for outdoor usage surely
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable Type (20 chars)
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
58

Thread Tags

Tags Tags
cable type

Advert

Thread statistics

Created
hightower,
Last reply from
7029 dave,
Replies
58
Views
5,374

Advert