I've been trying to locate anything in the regs that say this can't be done, but can't see anything.

Basically I have a 3kw oven on a 4mm T&E cable going to a 32A MCB (Cable is clipped direct in loft to consumer board, and not covered by anything en-route - property is a bungalow). The isolator already has 1 socket, however a requirement has occurred to have a second socket for a built in Microwave (800W). The first socket is in use on the kitchen worktop, this 2nd socket will be hidden away behind the cooker and microwave.

The circuit can handle the extra load, but is it allowed under the regs to have more than one socket on a cooker circuit. Yes I could just spur off the ring, but the nearest socket is on the other side of the worktop and I'd have to chase out a substantial amount of wall to get it done, whereas this way I would only need to chase about half a metre.
 
You haven’t got a “cooker” circuit.

you’ve got a radial circuit, wired in 4.00mm with a 32A supply.
You can do what you like with the circuit, it doesn’t know the difference.
 
come off the cooker isolator to a 20A D/P switch above worktop. then down to socket. you then have accesible isolation of appliance.
 
  • Like
Reactions: Jim_e_Jib
you can add what ever you want to the circuit as long as it’s not overloaded there shouldn’t be an issue.
just bare in mind that if your changing the size of the conductors a sufficient means of isolation would be required.
 
come off the cooker isolator to a 20A D/P switch above worktop. then down to socket. you then have accesible isolation of appliance.
Wont you need to fuse down to account for the smaller cable? would an FCU be better than a 20Amp switch just asking??
 
Wont you need to fuse down to account for the smaller cable? would an FCU be better than a 20Amp switch just asking??
not necessarily as you have a downstream 13A fuse in the plug.
 
not necessarily as you have a downstream 13A fuse in the plug.
Of course how stupid of me dohhhhh, what about protection of the cable to the socket though? brain in overdrive, but then again the plug fuse should take care of that issue, dunno whats wrong with me today , to much wine maybe that's my excuse.
 
the cable itself cannot be overloaded due to the 13A plug fuse. the 32A MCB protects it from short circuit. as in a fixed load scenario.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Can you have more than one socket on a cooker circuit ?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
vwes59,
Last reply from
telectrix,
Replies
7
Views
9,341

Advert