Hello I’ve bought a Clarke ceramic heater it’s a 110v and it’s got a 32amp plug on it , would it be possible to connect it to my 110v transformer via a (32amp socket to 16amp plug ) fly lead is that safe or do I need to plug it to an isolator before going into a 110v transformer
Can you help
Cheey
 
It probably has a 32a plug for a reason so without knowing the wattage or current rating no you cannot plug it into a 16a converter
 
Hello I’ve bought a Clarke ceramic heater it’s a 110v and it’s got a 32amp plug on it , would it be possible to connect it to my 110v transformer via a (32amp socket to 16amp plug ) fly lead is that safe or do I need to plug it to an isolator before going into a 110v transformer
Can you help
Cheey
It depends on the rating, if it is larger than 1.8kw it will take more than 16A, so it must use a 32A plug/socket.

Which raises the question what is the transformer rating? Most 110v site transformers are rated for 50% duty - so a 2kVA transformer is really only 1kVA continuous

If you are running a heater - which will be most of the time, your site transformer needs to be around 2x the heater rating or more.

If your heater is less than 1.8kw then you could change the plug to 16A or use a 16A to 32A lead or adapter.

If it is greater than 1.8kw then no, and your transformer is also likely to be too small.

I suspect they have used a 32A plug because the current will be more than 16A
 
  • Like
Reactions: loz2754
Deleted response!
 
Last edited:
It probably has a 32a plug for a reason so without knowing the wattage or current rating no you cannot plug it into a 16a converter
Hi Mathew the current rated current input is 22a so I guess the 16a is not enough, so how do I hook it up cheers
 
It depends on the rating, if it is larger than 1.8kw it will take more than 16A, so it must use a 32A plug/socket.

Which raises the question what is the transformer rating? Most 110v site transformers are rated for 50% duty - so a 2kVA transformer is really only 1kVA continuous

If you are running a heater - which will be most of the time, your site transformer needs to be around 2x the heater rating or more.

If your heater is less than 1.8kw then you could change the plug to 16A or use a 16A to 32A lead or adapter.

If it is greater than 1.8kw then no, and your transformer is also likely to be too small.

I suspect they have used a 32A plug because the current will be more than 16A
Hi the heater is max 2400w so I see 16amps is no good
 
Hi the heater is max 2400w so I see 16amps is no good
That's around 22A, and you would need something like a 2.5kVA continously rated transformer or typically a 5kVA site transformer
 
It depends on the rating, if it is larger than 1.8kw it will take more than 16A, so it must use a 32A plug/socket.

Which raises the question what is the transformer rating? Most 110v site transformers are rated for 50% duty - so a 2kVA transformer is really only 1kVA continuous

If you are running a heater - which will be most of the time, your site transformer needs to be around 2x the heater rating or more.

If your heater is less than 1.8kw then you could change the plug to 16A or use a 16A to 32A lead or adapter.

If it is greater than 1.8kw then no, and your transformer is also likely to be too small.

I suspect they have used a 32A plug because the current will be more than 16A
The transformer is 3kva and the heater is 2400w max power
How could I hook this up , it’s for a paint spray room built in an out building I have a few sockets in the room
 
The transformer is 3kva and the heater is 2400w max power
How could I hook this up , it’s for a paint spray room built in an out building I have a few sockets in the room
What type of transformer is it?

If it's a typical site one (usually a yellow box) there will be a rating label that gives the duty.

since 2400/3000 = 80% if the duty cycle is less than 80% then the transformer is not suitable.
 
That's around 22A, and you would need something like a 2.5kVA continously rated transformer or typically a 5kVA site transformer
Ok thanks everyone looks like I’ll have to find a bigger transformer, it’s my own fault I naught the heater assuming it would work on my transformer thanks for the help ?
 
  • Like
Reactions: DPG
What type of transformer is it?

If it's a typical site one (usually a yellow box) there will be a rating label that gives the duty.

since 2400/3000 = 80% if the duty cycle is less than 80% then the transformer is not
  • Intermittent rating of 3000W - duty cycle 5 mins on / 15 mins off.
  • Continuous rating of 1650W.
 
  • Intermittent rating of 3000W - duty cycle 5 mins on / 15 mins off.
  • Continuous rating of 1650W.
Yeah about what I though, actually 55%

If you get a 5kVA or larger one (or 2.5kVA continous ) it should come with a 32A socket outlet
 
As above with the suitable transformer it'll be fine
 


there's several on ebay. there's a used one bidding at £1. ends tomorrow..
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
32amp to 16amp fly lead
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
Gazzamataz,
Last reply from
telectrix,
Replies
14
Views
6,360

Advert