Discuss 32amp to 16amp fly lead in the UK Electrical Forum area at ElectriciansForums.net
Hello I’ve bought a Clarke ceramic heater it’s a 110v and it’s got a 32amp plug on it , would it be possible to connect it to my 110v transformer via a (32amp socket to 16amp plug ) fly lead is that safe or do I need to plug it to an isolator before going into a 110v transformer
Can you help
Cheey
It probably has a 32a plug for a reason so without knowing the wattage or current rating no you cannot plug it into a 16a converter
Can you help
Cheey
It depends on the rating, if it is larger than 1.8kw it will take more than 16A, so it must use a 32A plug/socket.
Which raises the question what is the transformer rating? Most 110v site transformers are rated for 50% duty - so a 2kVA transformer is really only 1kVA continuous
If you are running a heater - which will be most of the time, your site transformer needs to be around 2x the heater rating or more.
If your heater is less than 1.8kw then you could change the plug to 16A or use a 16A to 32A lead or adapter.
If it is greater than 1.8kw then no, and your transformer is also likely to be too small.
I suspect they have used a 32A plug because the current will be more than 16A
Hi the heater is max 2400w so I see 16amps is no good
The transformer is 3kva and the heater is 2400w max power
How could I hook this up , it’s for a paint spray room built in an out building I have a few sockets in the room
What type of transformer is it?
If it's a typical site one (usually a yellow box) there will be a rating label that gives the duty.
since 2400/3000 = 80% if the duty cycle is less than 80% then the transformer is not suitable.
That's around 22A, and you would need something like a 2.5kVA continously rated transformer or typically a 5kVA site transformer
Ok thanks everyone looks like I’ll have to find a bigger transformer, it’s my own fault I naught the heater assuming it would work on my transformer thanks for the help ?
  • Intermittent rating of 3000W - duty cycle 5 mins on / 15 mins off.
  • Continuous rating of 1650W.
Reply to 32amp to 16amp fly lead in the UK Electrical Forum area at ElectriciansForums.net
Hi, leading on from my question the other day about running the 3 phase compressor off my 8.5kW generator I have since got my hands on a 240v to 3...
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hello. I have a new oven. I understand completely that I need to get it installed by an electrician and will definitely do so but for my own...
6K
Hello fellow sparks, I’ve decided to go out on my own. Recently bought a little van and trying to get myself set up whilst keeping my costs as...