K
Kibo_769
Hi,
I've been digging and have nicked the outer sheathing of a 2.5mm SWA cable.
The protection and conductors are intact.
Would it please be possible to advise on how I can repair the outer sheathing by using heat shrink or any other suitable bonding agent to ensure no moisture flows in over time?
I will run an insulation resistance check before and after the repair.
Kibz
If you’re absolutely sure there’s no damage to the inner cores, or the breaks in the armour strands, then wrap self-amalgamating tape around it.
It’s more waterproof than insulating tape.
For something that looks more professional… get an underground torpedo joint….
Don’t make a joint, but encase the damaged section within the torpedo and fill with resin as normal.
Have you got a photo? Some repairs are more suitable depending on severity of damage.
Hi Littlespark, Thats great thanks for your reply.
Where can I purchase the self-amalgamating tape and the torpedo joint kit from?
Attached are the pictures let me know what you think?
I have never seen a swa cable with red bedding below the armour so I can only assume the bedding is also damaged and that red is conductor insulation. You are going to need professional help.
I hope that’s not a concentric, with the red core showing.
Could be a DNO job.
Slightly more mangled than I thought at first… a little bit of tape isn’t going to help.
Did you not see the yellow warning tape?
Could be a DNO job.
Think you may well be correct there.
Reactions: Jim_e_Jib
Looks like concentric dont it.
I’m not sure… certainly looks like a concentric, but the strands would be black??
Not entirely sure about that…
No I suspect you are correct mind you I can only find Chinese produced cables.
What depth was/is that cable at?
I have seen red strands.
Red strands as the outer wires??
I thought red inner, black stranded then bare stranded…. Or split concentric with red inner, then black and some green on the outer
I thought the same but I'm swayed by fact he knows it's 2.5mm and says he can IR it, suggesting he has control of both ends of it.
The current IR results would be a good start.
Definitely seen blue strands brown solid core, sure I've seen red strands got me thinking now maybe not.?
Tried zooming in could be red conductor, good old 2 core SWA.
Reactions: pc1966
It doesn’t look like like 2.5….
It needs professional repair, whatever it is.
If the OP could clarify when it gets looked at
Do we think the word 'slight' is underestimating things.
Yeah bit more than a nick more like a gash.
Hi All,
Thanks for all the comments. The cable was meant to be buried at 600mm but the person who laid in in that particular section skimped out at laid it at less than 300mm and the warning tape wasn't event 150mm above the SWA cable.
This cable has not yet been connected or energised so was able to check the ident. It is a 2.5mm SWA cable and was able to cut a small piece from the slack end. After the repair I will ensure the cable is installed to 600mm depth.
The pictures will illustrate the black sheath, the armour strands. You then have a red insulation inner sheath and then the individual 3 conductors Black, Grey & Brown).
This cable will be used for lighting only and the 2.5mm cable was chosen due to the long run of cable taking voltage drop into consideration.
Please let me know if the repair is still feasible?
Thank you all for your replies
  • Informative
Reactions: nicebutdim
A repair is always possible, but depending on how damaged it is in the segment it might need two joints and a new small section inserted.
But I would start by cutting mid-damage and seeing if it looks clean enough that it can simply be joined in a suitable torpedo style of resin joint. Something like this:
As the cable has not been installed yet you can easily do an IR test (having checked the far end is clear of any shorts, etc) to get an idea if it is OK even before you start cutting (which you should not do until you are ready with a joint to finish it).
Edit: I would try and simply part the cores, etc, without cutting through, it is best if you don't have actual joints and simply use the resin unit to allow it to be inspected and covered over if no real damage is seen.
Reactions: 123
It does have red bedding never seen that before.
Could be a DNO job.
see y last thread, the inner insulation is red. see the pics. Ill give it a thorough inspection first
As @pc1966 said it's likely you won't have to completely cut it and start again, probably just get a torpedo case around it if IR readings are ok.
They are actually quite easy to use. This video shows the whole process.
Absolute worst case is two joints and a new section, like this one I had to do:
Reactions: Kibo_769
Thanks pc1966 - ill clean the muck off remove the damaged outer sheathing and then inspect and use the resin cover without cutting the cables if there is no visible damage. ill post pics once completed
Thanks littlespark - ill clean the muck off remove the damaged outer sheathing and then inspect and use the resin cover without cutting the cables if there is no visible damage
When he said nicked the outer sheath. i was thinking a small cut and was going to say just wrap a load of electrical tape or heat shrink to protect the SWA from getting rusty.. I guess this highlights the problem with forums, one persons nicked it with a spade is another persons mashed it with a spade..
Thanks Tim - thats is really useful. ill inspect it and send in the results. wher di you purchase the torpedo from? CEF dont have any in stock at the store so will need to order it in
I got it from one of my usual local merchants.
Screwfix sell them, search "resin joint"
I wouldn't recommend insulating tape. Self-amalgamating tape is more appropriate.
Email
Time zone
Last seen
Slight damage to SWA cable
Kibo_769,
philectrical,