If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
My friend has a garage door that when opens turns on a floodlight.

He know wants it to turn on another light in the garage as well as the floodlight.

The problem is this garage light is already on a plate switch, if the garage light was simply connected to the control panel then the plate switch would then operate the flood light as well, this needs to be avoided. (see pic below)

Does anyone have a simple solution? Is there anyway to allow the line current only to flow from the panel and stop the back flow of current to the panel from the plate switch?

garage.jpeg
 
Last edited:
use a relay. energise with the plate switch, use 1 piair of contacts N/O to switch gaage light. at same time use a pair of N/C to isolate floodlight from switch.
 
  • Agree
Reactions: Davisonp
Contactor.
I was just about to add, can I use a contactor or relay! However, having just dealt with domestic electrics I am unsure how these work or would be connected into the circuit. If anyone could expand a little that would be great, thanks.
 
230V coil relay. energise with switch.pick a set of contacts.feed to common, N/Oto garage light, N/C tobreak switch feed to flood.
 
I think a diagram may be needed..... RICHARD!! :D
 
If the plate switch isn't being used as 2 way you can use that.

Connect the light to Common,
Feed from the control panel to L1
Permanent feed to L2
 
  • Like
Reactions: HappyHippyDad
If the plate switch isn't being used as 2 way you can use that.

Connect the light to Common,
Feed from the control panel to L1
Permanent feed to L2
Snowhead! That is so simple yet effective. Many thanks :)
Ps.. It is being used as 2 way (I was just lazy in my drawing), however he never uses the other switch so I can just eliminate it.
 
NOOOOO! Not this again! Is this the same door or another one?
If the light supply and door opener supply are on different circuits you can't do this as it ties the two circuits together. Even if on the same circuit, the door opener cannot be isolated using its means of isolation; the neutral remains connected and the line is disconnected only by a functional switch. You must use a relay.
 
  • Agree
Reactions: Shoei

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What can be used to stop back flow of current?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Lucien Nunes,
Replies
9
Views
1,537

Advert