Been having a debate with a mate this afternoon about a circuit in his house.
The circuit is a radial with 16 amp mcb that was previously used to feed his immersion heater that was removed when a boiler was fitted- he doesn't have a radiator in the conservatory and cant afford one to be fitted. he is going to divert the cable from his kitchen where the Cu is out the wall into the conservatory. Then get the electricians at his work to give it the once over.
He is of the view the way to wire a 3kw electric wall mounted heater in is to use a 13 amp FCU. I am saying no, have to use a DP 20 amp switch fed from breaker. 3kw is just over 13 amp 3000/230 = 13.04 amps and given the circuit is a radial fed with a 16 amp breaker with nothing else on it, the fcu is doing nothing of use and is un-necessary. Also adding 3kw heaters onto a ring will likely overload it.
This is the bit that then made me chuckle, he has recently been on a job - hes a surveyor for social housing outfit where the electricians have put 2 separate 3kw heaters on 13 amp fcu's joined to the rfc during refurbishments of some social housing units. He seemed oblivious to the issue of having a couple of 3kw heaters plus the other household appliances on the one 32 amp ring!
It makes you wonder how there haven't been more grenfell fires if the supposed people in charge of quality and standards sign off things like this. Of course given the low power draw of a lot of modern stuff its possible that the circuit might take the 2 heaters in the social housing example, but you don't know if the tenant will plug hoovers, irons and god knows what else in when the heating is on max.
 
Dub pole switch, maybe an fcu 30 yrs ago when they could actually cope with 13A but not the tat you get now.
 
Dub pole switch, maybe an fcu 30 yrs ago when they could actually cope with 13A but not the tat you get now.
I think some of the better quality fcus would hold a good load but i have seen far too many cheap accessories that seem to have ever thinning pieces of metal in them, You also dont know anymore where a lot of the stuff is made as people cash in on the names and make crap stuff.
 
If the heater came with a 3 pin plug, I'd use it. If no plug, then I'm not a fan of 3kW loads in FCU either. And just be be a complete Abacus, the 3kW heater will likely be rated that at 240V :) .
 
  • Agree
Reactions: 123
I have installed many electric UFH systems where the total load is around 12 amps and had many issues over the months after of the sw/f/spur over heating and welding the fuse in or just failing.... 20 amp dp switch all the time.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gavin John Hyde

Esteemed
Arms
Patron
~
Joined
Location
Somerset
Website
http://www.sulis-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Sulis Electrical Services Ltd

Thread Information

Title
20amp DP switch or fcu for 3kw heater?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Gavin John Hyde,
Last reply from
ashrow,
Replies
6
Views
21,357

Advert