Been having a debate with a mate this afternoon about a circuit in his house.
The circuit is a radial with 16 amp mcb that was previously used to feed his immersion heater that was removed when a boiler was fitted- he doesn't have a radiator in the conservatory and cant afford one to be fitted. he is going to divert the cable from his kitchen where the Cu is out the wall into the conservatory. Then get the electricians at his work to give it the once over.
He is of the view the way to wire a 3kw electric wall mounted heater in is to use a 13 amp FCU. I am saying no, have to use a DP 20 amp switch fed from breaker. 3kw is just over 13 amp 3000/230 = 13.04 amps and given the circuit is a radial fed with a 16 amp breaker with nothing else on it, the fcu is doing nothing of use and is un-necessary. Also adding 3kw heaters onto a ring will likely overload it.
This is the bit that then made me chuckle, he has recently been on a job - hes a surveyor for social housing outfit where the electricians have put 2 separate 3kw heaters on 13 amp fcu's joined to the rfc during refurbishments of some social housing units. He seemed oblivious to the issue of having a couple of 3kw heaters plus the other household appliances on the one 32 amp ring!
It makes you wonder how there haven't been more grenfell fires if the supposed people in charge of quality and standards sign off things like this. Of course given the low power draw of a lot of modern stuff its possible that the circuit might take the 2 heaters in the social housing example, but you don't know if the tenant will plug hoovers, irons and god knows what else in when the heating is on max.
 
Dub pole switch, maybe an fcu 30 yrs ago when they could actually cope with 13A but not the tat you get now.
I think some of the better quality fcus would hold a good load but i have seen far too many cheap accessories that seem to have ever thinning pieces of metal in them, You also dont know anymore where a lot of the stuff is made as people cash in on the names and make crap stuff.
 
If the heater came with a 3 pin plug, I'd use it. If no plug, then I'm not a fan of 3kW loads in FCU either. And just be be a complete Abacus, the 3kW heater will likely be rated that at 240V :) .
 
I have installed many electric UFH systems where the total load is around 12 amps and had many issues over the months after of the sw/f/spur over heating and welding the fuse in or just failing.... 20 amp dp switch all the time.
 

Reply to 20amp DP switch or fcu for 3kw heater? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
260
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
228
Done a few EICR's recently and having a blonde moment regarding storage heaters. All storage heaters in the property are rated at 1.5kw and fed...
Replies
9
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock