Davey1988

Hey guys

The air con unit has a start current of 83amps and a running load of 13amps. It's currently wired in 6mm which takes 47amps which is obviously lower than 83amps, would you say this is OK Aslong as the mcb protects the cable.

Saying that if I used a 20amp type C mcb it would take 160 amp to trip within 5 sec and would take 20 secs with 80amp which should be enough time for the starting current. But after its loaded I'm worried that it will take 60 seconds to trip on 50 amps which is not acceptable for the cable.

Any advice or help on this?
 
A lot of these air con units these days are soft start not taking the current like they used to, personally i would have it on a C16
 
This would still feed 50 amps for 30 seconds. Without disconnection.

In a unlikely event of the overloading to 50 amps Constantly wouldn't this cause a problem. Do u see where I'm coming from. Is this allowed
 
Slight bit of over-thinking going on here.


A-C running current 13a.
Cable protection 20a.
Cable rating 47a.
 
  • Like
Reactions: 2 people
So are you saying I can install this in 2.5 since cable protection is 20 amp.

Seems unsafe and wrong.

Edit. I'm wanting to know of the logics of this that's all.
 
So are you saying I can install this in 2.5 since cable protection is 20 amp.

Seems unsafe and wrong.

Edit. I'm wanting to know of the logics of this that's all.

you select a cable thats capable of carrying the nominal continuous running current of the equipment , which is 13A , not the short duration of initial over-current , which may be 50A and upwards.

whether that cable is to be 2.5mm will be dependant on circuit length & volt drop amongst other factors.
 
  • Like
Reactions: 2 people
Ah I see. Since the length is 15 meters in 2.5 with 13 amps. It's 2.8899 volt drop which is fine and cable factors are fine which does not derate the cable below 20 amps.

Would I do the calcs on the start up current also or is the expected constant current flow is what we work from?

Would you install it in 2.5 going from the figures I've provided.
 
Last edited by a moderator:
So are you saying I can install this in 2.5 since cable protection is 20 amp.

Seems unsafe and wrong.

Edit. I'm wanting to know of the logics of this that's all.

Of course you can!

Cable size calculations are based on Ib, not on the peak inrush current!

If we based cable size on inrush current we'd all be wiring LED downlights in 6mm T&E

You are a qualified electrician aren't you?
 
  • Like
Reactions: 1 person
Of course you can!

Cable size calculations are based on Ib, not on the peak inrush current!

If we based cable size on inrush current we'd all be wiring LED downlights in 6mm T&E

You are a qualified electrician aren't you?
be nice, his profile says he is a trainee
 
Am I right in saying the heat and cooling kw is not load kw on the air conditioning units.

20141020_141353.jpg
 
One of the reasons I was baffled as it was installed in 6mm. Which is way to big. Either it stated on manufacture instructions or they didn't have a clue
 
  • Like
Reactions: 1 person
One of the reasons I was baffled as it was installed in 6mm. Which is way to big. Either it stated on manufacture instructions or they didn't have a clue
im betting they dont have a clue, if i remember right 6mm is good for around 40ish amps

not 81amps if thats what they were looking at

might have been manufacters instructions but i find that a bit strange
 
Heating and cooling capacity is exactly what it says on the tin.

It's the section labelled power input that concerns the electrical power input, as you can see it is expressed in both KW and Amps.

You'd normally want to see a power factor quoted on there too.

The starting current will help you to select a suitable OCPD for the supply to avoid tripping due to the inrush.

Taking a rough approximation your 20A mcb will see an inrush current 4X it's rating, and a type C I think is rated for inrush up to 6X it's rating.
 
One of the reasons I was baffled as it was installed in 6mm. Which is way to big. Either it stated on manufacture instructions or they didn't have a clue

Is it an old supply which has been re-used for a new unit at some point in time?

It is quite possible that a previous AC unit needed a 32A supply and when it was replaced they just changed the mcb.

Or the supply was installed for 32A with incorrect information from the AC contractor and had to be down rated to 20A when they had fitted the unit
 
Do you wanna even know the worst bit. It had a 32amp type b.

What's wrong with that? It makes a lot more sense of the 6mm T&E if it has a 32A B type.

The MCB is there to provide fault and overload protection for the cable, it does not provide provide protection for the appliance.

A 32A type B will be fine with that starting current and sounds right for providing protection for 6mm T&E so no problem.
 
81amp start current....

Wouldn't it trip immediately

Type B mcbs are designed to withstand a starting surge between 3 and 5 times their rated current.

81/32=2.53 so it will be fine with that startup surge.

Is this an existing installation or a new installation which has never been switched on? If it is an existing installation and it is working then you don't need any calculations or theory, the mere fact that it is working without the MCB tripping proves that there is no issue with the startup current.
 
There's a short in the circuit some where even with the air con disconnected, and the God knows what else it spured off to which it is easy running a new supply to the air con.

20amp type C with 2.5 flex would be fine.

Appreciate the help BTW. I know it's hard to get a bit of advice sometimes from people on here. They think I'm testing their ability or something.
 
There's a short in the circuit some where even with the air con disconnected, and the God knows what else it spured off to which it is easy running a new supply to the air con.

20amp type C with 2.5 flex would be fine.

Appreciate the help BTW. I know it's hard to get a bit of advice sometimes from people on here. They think I'm testing their ability or something.

What exactly is the point of this thread? what do you want to find out?

If there is a fault on the circuit then find the fault and repair it. If only god knows what else has been spurred off from the circuit then either go and ask him about it or trace the circuit yourself and find what has been spurred from it.

You need to do some proper calculations before just assuming 2.5mm flex and a 20A MCB will be OK, can you meet the disconnection times with this arrangement? Is flex the most suitable cable to install? What containment will it be installed in or how else will it be supported?

Your profile says you are a trainee? is this correct? if it is then your mentor should be looking over your work and you shouldn't have to resort to asking cryptic questions here to find out what you should be doing.
 
  • Like
Reactions: 1 person
We are wiring new heating systems for our local council and the spec is to supply the air source units with 6mm on B32s and the rating of the unit is only 11.5A!
 
Wired the air con with 2.5 flex and 20a type C. Works fine.

Who ever does their specs want shooting. Over estimated. Probz because it's not their money it's the tax payers.
 
Wired the air con with 2.5 flex and 20a type C. Works fine.

Who ever does their specs want shooting. Over estimated. Probz because it's not their money it's the tax payers.

Sometimes over-speccing is to allow for future changes to installed equipment....it's called thinking ahead/future proofing.
 
Wired the air con with 2.5 flex and 20a type C. Works fine.

Who ever does their specs want shooting. Over estimated. Probz because it's not their money it's the tax payers.

Just because it works fine it doesn't mean it is right?

Did the Zs comply on your new circuit? Have you used suitable fireproof support for the flex if needed. Is the flex LSF insulated if needed?
 
Be careful with your VD calcs though. When selecting the cable for CCC, the running current is what counts because it is a thermal limitation and the cable does not heat up significantly during the short starting period. But the VD applies just as much to the starting current and if it is excessive at the higher figure the compressor might not start at all, especially if it has recently been running and is now trying to restart against head pressure.

So where oversize cables seem to have been specced, it might be to satisfy the manufacturers maximum permissible VD during starting.
 
  • Like
Reactions: 1 person
Wired the air con with 2.5 flex and 20a type C. Works fine.

Who ever does their specs want shooting. Over estimated. Probz because it's not their money it's the tax payers.

Floating on the same lines as Lucien here ....

When speccing a cable type and mcb rating for motors - things to be taken into account:-

-The frequency of start
-The duration of the start
-Your calculated ELI relative to you mcb type meeting the starting current without tripping

The first 2 points are relatively rare in the domestic and small commercial to be an issue but as in my area of work is crucial as the larger high inertia motor loads take some extra considerations when designing.

The manufacturers instructions now should specify a mcb rating to protect their product like in OP's case and this may specify a 32(b) for a number of reasons, manufacturers tend to play extra safe and can over-spec products requirements to account for worse case scenario's because they lack many neccessary info to give a better guidence.

Having said that if this is a dedicated circuit then protecting the cable for O/L may not be required as the unit should have O/L protection for the motor and thus could be classed as a fixed load circuit meaning you may be able to keep say a 32a(b) if requested by the manufacturer but only supply it on a 2.5mm cable (installation calcs allowing of course).

Manufacturers sometimes use the term 'recommended' mcb rating and this is just that 'a recommendation' - if you can calculate it diferently and prove the lower rating won't nuisance trip then do so but if on the rare occasion you are asked to justify your calcs then be prepared to do so.

To note here and a trap often fallen into is the trip curves of mcb's

Example lets say a 10amp type C has a tripping characteristics of 5ln - 10ln and your motor has a 6amp flc but a peak inrush of 55amps which is 5.5ln relative to this mcb, now the mcb can trip with a current anywhere between 50a and 100a, any higher than 100amp inrush should trip it 100% of the time but when you get close to it lower limit the frequency of tripping here become very low. Having said this if it can trip at all and your inrush falls within the range then you should either increase the mcb type of the mcb ampage until the chances of inrush tripping is 0%. Not forgetting to still meet ELI and VD.

Your peak inrush should be lower than the lowest trip 'ln' of the mcb many think that if you inrush is within the 2 'ln' values of the mcb then this is ok.... the mcb does not trip at a certain ampage repeatedly, you are given the lower and upper tolerances of the mcb and it may trip at 51 amps on one occasion but next time it may trip at 99amps (in relation to my example).
 
Last edited by a moderator:
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Air conditioning unit on a type C mcb
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
Davey1988,
Last reply from
davesparks,
Replies
30
Views
18,917

Advert