I'm going to be wiring an extension(3 floors) to a retail unit which will need a new supply as the demand is quite high already(high 80's on all phases through the day).

Anyway I've totaled up the loads for each floor into Lighting and Power and Storage Heating but I'm not too sure how to apply the diversity to it, can anyone help?

Cheers
 
100% of the lighting
100% of the next largest load (probably the storage heaters?)
40% of everything else

Is how I would do it I think!
 
Just checked the On-site Guide and found this:

Lighting - 90% of total current demand
Heating - 100% of largest appliance & 75% of the rest.
Power - 100% of largest point 70% of every other point.

Lighting - I take it that means add all my lighting points up and take away 10% to give total.

Heating - Straight forward.

Power - Do I count up the number of Ring Mains and use the first Ring at 100% and the others at 70%?

If I do that I end up with this:

Lighting - 6400w to 5760w

Heating - 27200w to 21760w

Power - 11 Rings at 32A = 61440w

What do you think, does that look anywhere correct?

Cheers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Applying diversity?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
andrew692003,
Last reply from
andrew692003,
Replies
3
Views
1,939

Advert