Cabling above suspended ceiling the 600x600mm type tiling ceilings.
Basically cables routed above ceiling’s no fixings, laid on top of framework, the gap above the tile is approximately 50mm, nearly impossible to get tile out.
The Install of these cables between 1969 until present day, I’m wondering if theses ceilings are acceptable for compliance with fire regulations.
I know it’s not compliant now but compliant “Partly” when installed.
What code would you give on a EICR…& advice to Client
 
Comply with 'fire regulations' or do you mean BS7671.
You cannot use the ceiling grid for cable support no matter when it was installed.
 
Comply with 'fire regulations' or do you mean BS7671.
You cannot use the ceiling grid for cable support no matter when it was installed.
Agree this install was done in the days when chucking cables over ceilings were the Norm. Also I’m not using the grid for cable support
 
Cables should not be thrown across suspended ceilings it was never the norm.
 
Of course I see it virtually every day but it doesn't mean it is correct.
 
Since the cables are incorrectly supported then you can code it accordingly for that departure. Then advise the client based on your findings - either some containment or additional support in line with the current regs should be installed.
 
I would say 99% of jobs you will come across daily as a working sparks will not fully meet current regulations. Especially jobs that have been modified by every tom dick and harry over a long period of time. Cables slung in on-top of a false ceiling happens every day and will continue to happen every day as price is always the main driving factor.
Can you imagine telling someone you need to fit a whole bunch of galv tray above a ceiling just to install an extra socket? you simply would never get any work.
I don't do shop fitting anymore but when I did we were 'Told' to just lash the cables above the ceiling as quick as possible. As a 17 year old you did what you were told ( even if you knew it was a complete lash-up) and I bet a months wages nothing has changed since
 
I would say 99% of jobs you will come across daily as a working sparks will not fully meet current regulations. Especially jobs that have been modified by every tom dick and harry over a long period of time. Cables slung in on-top of a false ceiling happens every day and will continue to happen every day as price is always the main driving factor.
Can you imagine telling someone you need to fit a whole bunch of galv tray above a ceiling just to install an extra socket? you simply would never get any work.
I don't do shop fitting anymore but when I did we were 'Told' to just lash the cables above the ceiling as quick as possible. As a 17 year old you did what you were told ( even if you knew it was a complete lash-up) and I bet a months wages nothing has changed since
All true and we all come across it regularly. But for the purpose of the report then Cliff should code it accordingly and offer the advise to the client based on the regs. It's up to the client then to decide if they want it improving.
 
Last edited:
All true and we all come across it regularly. But for the report then Cliff should code it accordingly and offer the advise to the client based on the regs. It's up to the client then to decide if they want it improving.
and this is the problem , even if Cliff says the current install is Code steamingpileofsh!t the client is under no obligation whatsoever to do anything about it. they can just leave it as it and carry on regardless
 
  • Like
Reactions: cliffed
and this is the problem , even if Cliff says the current install is Code steamingpileofsh!t the client is under no obligation whatsoever to do anything about it. they can just leave it as it and carry on regardless
Yep, I agree this is the failing of the system though not Cliff. All he can do is report what he finds and advice accordingly to the requirements.

We all know the client is not going go to the expense of having the work done. But if there was ever a fire and the ceiling came down and a fire fighter was killed because he/she got caught up in all the hanging cables then there will be an investigation, a paper work trail that will eventually lead to who is liable.
 
Yep, I agree this is the failing of the system though not Cliff. All he can do is report what he finds and advice accordingly to the requirements.

We all know the client is not going go to the expense of having the work done. But if there was ever a fire and the ceiling came down and a fire fighter was killed because he/she got caught up in all the hanging cables then there will be an investigation, a paper work trail that will eventually lead to who is liable.
Cheers Client will not have the necessary works for requirement, thanks all for your input.
Also it’s the fault on all Party’s who over the years & lately have just not complied… just chuck it over & way we go
 
  • Like
Reactions: Intoelectrics

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Cabling above suspended ceilings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
cliffed,
Last reply from
Dustydazzler,
Replies
13
Views
6,261

Advert