I was on small touring caravan site yesterday looking at a caravan electrics for a client.

I've not done any caravan site work but the onwner asked me to look at a few things whilst I was there.

The site has only one hookup point with four commando blue sockets on 16a RCBO's in a hookup box mounted on a wooden post. This has been fed with 6mm 3 core swa from bs3036 rewirable which is on a tnc-s earthing arrangement. There is no earth rod at all.

Obviously I realise under the regs exporting tnc-s to a caravan hookup point is an absolute no no. I intend to disconnect the 3rd core used currently for the earth and probably run it in parallel with the live and sleeve it in brown. The armour I will leave connected at the supply end and disconnect from the hookup end as this is an extraneous conductive part.

I will put an earth rod in at the hookup and run it into the hookup supply unit. Would it be acceptable to run the earth rod into an adaptable box mounted low down on the post or does it have to be an earth pit box?
Your thoughts on any of the above would be appreciated.
 
Is there a reason you don't want to use a pit box? I always question why does someone want to do away with something that is designed for the specific task, and adapt something that isn't.

Obviously from your post you seem to know what your doing so there must be a reason you want to use your method. As long as your can protect you connection as to the Regs section 526 and you label it to Reg 514.13.1 then I see no problems with that.
 
asd above, but why do you want to parallel up the 3rd core with the live. serves no useful purpose, as the neutral will still be 1 core. unless you want to put sockets on separate fuses.
 
The post is surrounded by grass so I just thought it would look nicer not having an inspection pit dug into it. The only reason for running the third core in parallel is so I have somewhere to terminate it at both ends rather than cut it.
 
so you should leave it earthed at 1 end ( the TT end ) . terminate the other end into a blind connector.no reason why not have 2 separate lives, each feeding 2 sockets.
 
Last edited:
cadspark, a plastic inspection pit box (SERPT205, £25.85+VAT) will give better protection, whilst being easy to fit. If you don't want to use this then an earth rod box (MECB75G, £5.49+VAT) is the next best alternative. The part numbers and prices quoted are from the current Senate Electrical catalogue.
 
I was on small touring caravan site yesterday looking at a caravan electrics for a client.

I've not done any caravan site work but the onwner asked me to look at a few things whilst I was there.

The site has only one hookup point with four commando blue sockets on 16a RCBO's in a hookup box mounted on a wooden post. This has been fed with 6mm 3 core swa from bs3036 rewirable which is on a tnc-s earthing arrangement. There is no earth rod at all.

I would place an electrode iat the origin of the distribution circuit along with an additional electrode at the hook up.

Obviously I realise under the regs exporting tnc-s to a caravan hookup point is an absolute no no. I intend to disconnect the 3rd core used currently for the earth and probably run it in parallel with the live and sleeve it in brown. The armour I will leave connected at the supply end and disconnect from the hookup end as this is an extraneous conductive part.

This would contravene Reg 524. I would leave as an earth and connect it to an electrode at the supply end.If volt drop is an issue you could use it as a neutral.

The armor is an exposed conductive part, connect it at the supply end and also to the additional electrode at the hook up.

I will put an earth rod in at the hookup and run it into the hookup supply unit. Would it be acceptable to run the earth rod into an adaptable box mounted low down on the post or does it have to be an earth pit box?
Your thoughts on any of the above would be appreciated.

Regards

Chris
 
Chris.....If you connect the armour to both supply earth AND the electrode you will introduce the TNCS......bit pointless really.

Maybe my post was not too clear, i said supply end, not the tnc-s supply, the distribution cable will be connected to two electrodes:

Divorced entirely at the origin of the distribution circuit.

1, at the supply end of the Distribution
2, at the hook up

This way no potential is taken out to the hook up.

Chris
 
Last edited:
can you use a rod and connect it striaght to the sockets, for some reason ive always thought it needed to be though a protective device.

Also wouldnt using the the extra cable as a live reduce voltdrop ? maybe not needed but....
 
Hi
Earth rod box/cover and "safety electrical connection" label acceptable.
Armour MUST be earthed at supply end - any fault will introduce TNC-s fault to neutral and therefore not acceptable to TT installations
ONLY phase and neutral to be transferred to TT system and separate earth rod AND RCD ESSENTIAL to be at the hookup end.
TEST before commissioning for use and values for RCD trip times must now comply with 17th ed:2008 values.

David
 

Reply to Caravan hookup on tnc-s in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Replies
0
Views
881
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock