Adie moore

went to a house today, it was a tt system with no rcd protection anywhere. Ze was 143ohms, Zs on a socket ring was a bit better. mcbs were old bs 3871 push button conversations. thing is, the overhead supplying the house had been replaced about 4 years ago, nice new service head ripe for a PME upgrade. I know it's not their job but come on.
 
It's not their job to connect a customers system to their earth. Maybe one is provided at the head ?
 
I know but when I explained it to the chap and he said to me " well why didn't they just tell me to get It done while they were here " I didn't have an answer for him. how would I tell if their was a earth provide, I'd expect to have to get the dno out or can I open it up and have a look if theirs a link between the N and E?

edit; even if their is a link I would be happy about just assuming it was OK to shove my earth in their.
 
Test it and see what Ze you get [Or not as the case may be].
 
The DNO are under no obligation, if the earthing arrangement is TT.
 
I know they don't. but while they were their, if they gave a ----, they could have just said, oh buy the way sir if you want to get a local electrician in their's an earth connection available now. As it is their is no earth fault protection.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
do the DNO have a duty of care
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Adie moore,
Last reply from
Adie moore,
Replies
5
Views
1,429

Advert