TCES

I have been asked to quote for connecting up an 8.5kW electric shower unit in a hairdressing salon for use over a standard hairwashing sink. (The potential customer has already bought it). The salon is a former shop and open plan. Therefore no physical barrier is present between the sink & shower witha standard length flexi hose and socket outlets in the salon. There is no existing circuit for the shower so therefore I would have to install cable, RCD, isolator etc and be able to issue an installation certificate. Earthing and bonding are present and to current requirement of 7671.

I have to say that I am not at all comfortable with this, but this is commercial, not domestic and it is not a bathroom. I cannot find anything in BS7671 appropriate to the situation. I could RCD the other circuits in the location as an obvious precaution but I would be interested if anyone else has had a similar situation and any guidance regarding this generally. I could do with someone quoting chapter and verse !

Cheers
 
I didn't see any next to it. What bothers me is the mains pressure and the long flexible hose and shower head so they may not need to be close to be vulnerable !
 
Surely this comes under special locations as there is a shower invlolved, just because it is not in a cubicle or over bath doesn't mean it should be treated any differently.

I would draw up a contract with the customer saying they want it installing in said location with a list drawn up off possible risks in the future.

Even noting said contract in the departures section of the certificate.

Far from ideal but just about every other hairdressing salon in the country has this set up yet you never seem to hear of anyone being killed or electrocuted in them.
 
  • Like
Reactions: 1 person
I didn't see any next to it. What bothers me is the mains pressure and the long flexible hose and shower head so they may not need to be close to be vulnerable !

Well what about the zones? >0.6m from shower is zone 2. Sockets <3m from zone 1?
 
The difference here is that in a shower the person taking the shower is usually not clothed, and dripping wet - not a good situation for touching electrics.

In the salon its not the same, Ok, someone's hair is wet but generally they won't be holding the shower head and the won't be wet head to foot.

Appreciate that sockets need to avoid being drenched, just like sockets in a kitchen, so obviously a safe distance and unlikely to be splashed. How is this different from a kitchen sink (say), theres plenty of kitchen taps now that are just as good as a shower head for splashing water around!
 
i don't think that the normal rules for special locations ( bathrooms) apply in this case. reasoning being that the client and the hairdresser are not wet, standing in water, or in any way likely to be injured by the use of a shower used basically as a tap.common sense would prevail here.
 
  • Like
Reactions: 1 person
Surely this comes under special locations as there is a shower invlolved, just because it is not in a cubicle or over bath doesn't mean it should be treated any differently.

incorrect , the bs7671 definition of a bathroom ( and the classification of special location )
is relevent only to bath & shower basins , where the increased risk is from being stood wet & naked.
a sink with overshower is outside this catagory and is not bound by the min 3mtr skt rule nor the rcd protection of all circuits in the location.
which is why there are no zone 0 , 1 or 2 for sinks.
;-)
 
Last edited by a moderator:
  • Like
Reactions: 3 people
biff, that's basically what i was trying to say, but in different words. bit tired, having been to b-i-l's for beers etc,.
 
I take your point, but do I regard this as a shower or a wash basin? There is no base or bath to stand in. :confused: This is the connundrum
 
I take your point, but do I regard this as a shower or a wash basin? There is no base or bath to stand in. :confused: This is the connundrum

well if you do class it as a special location then you are going to have alot of trouble making sure all sockets are 3 mtrs from all sinks in a hair salon.
just not feasible.
 
but do I regard this as a shower

No, you don't see anyone standing barefoot and naked in the middle of a hairdressers in a tray having their hair washed.

or a wash basin?

It's a Backwash unit where the customer is seated with clothes and shoes on and their head is tipped backwards over a bowl with a neck rest on it.
WHITE HAIRDRESSER SALON BACKWASH SINK USED | eBay



This is the connundrum

Definitely NOT a connundrum, it's black and white, if it wasn't there would be a special location for Hairdressing Salons.


If you are fitting the shower you need to be aware of the regs to prevent backsiphoning from sink to shower hose.
 
Last edited:
on the other hand, a few shocks would give rise to some funky hairdos, no extra charge.
 
  • Like
Reactions: 1 person
Thanks to all for your replies. In the end I contacted NICEIC Technical who stated that I should regard it as a 'shower' even though it doesn't have a stand in tray and that the zones apply along with RCD protection on all circuits. No socket outlets within 3 metres of zone 1, spur units allowed outside zone 2 etc.

Went in to see the client to explain (hard work as he had no concept of complying with rules or regulations). Turned out he has an Ariston europrisma unit plumbed in, but with a leak. He thought fitting a shower would be cheaper that replacing the ariston ! Now he is replacing the Ariston.

All the Best
 
Thanks to all for your replies. In the end I contacted NICEIC Technical who stated that I should regard it as a 'shower' even though it doesn't have a stand in tray and that the zones apply along with RCD protection on all circuits. No socket outlets within 3 metres of zone 1, spur units allowed outside zone 2 etc.

Went in to see the client to explain (hard work as he had no concept of complying with rules or regulations). Turned out he has an Ariston europrisma unit plumbed in, but with a leak. He thought fitting a shower would be cheaper that replacing the ariston ! Now he is replacing the Ariston.

All the Best

here we go again. niceic rewriting the rule book.
 
  • Like
Reactions: 2 people
Thanks to all for your replies. In the end I contacted NICEIC Technical who stated that I should regard it as a 'shower' even though it doesn't have a stand in tray and that the zones apply along with RCD protection on all circuits. No socket outlets within 3 metres of zone 1, spur units allowed outside zone 2 etc.

so the nic cant be arsed reading the regs book properly.
great.
i'd rather get tech advice from Asda.
;-)
 
  • Like
Reactions: 1 person
Thanks to all for your replies. In the end I contacted NICEIC Technical who stated that I should regard it as a 'shower' even though it doesn't have a stand in tray and that the zones apply along with RCD protection on all circuits. No socket outlets within 3 metres of zone 1, spur units allowed outside zone 2 etc.

Wonder what Lord Cable would say on this subject? Should ask him at next week's ELEX.

Might have to get a job on the NICEIC Tech line, sounds like you just need to sit there and make things up! :smilielol5:
 
  • Like
Reactions: 1 person
If that is the best bit of advice the NIC can give then all hair salons should close, FFS are they putting electrical trainee on their technical support line now?

Ben
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Hairdressing salon. Electric shower unit 8.5kW over sink !!
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
TCES,
Last reply from
Brendan976,
Replies
20
Views
14,974

Advert