I was asked to look at a storage heater that wasn't working.

Set up is a combined double row MEM board with lighting and power on top row, and 3 way split row on the bottom for water heating, storage heaters and panel heaters, each with their own double pole mainswitch and neutral bars.
A couple of storage heater points have been changed to the panel heater side for different heaters.

The problem was a faulty 20A double pole switch for the storage heater in question.

Now, for the quiz.
Having turned off the mainswitch for all the storage heaters, but not the panel heater side, and the timeclock not turned on, I was getting 230v between neutral and cpc at my switch. WHY?

I was not getting power between live and cpc, or live and neutral.... only neutral - cpc

Suggest answers in your replies.
 
I would've hazarded a guess at a shared neutral from an energised circuit? Sharing say from the lighting circuit so even when the heater circuit was isolated, it was still getting power from the live lighting circuit?

It's the only way I can see it, getting power from a different source? Not done a lot of borrowed cables so my understanding may be off?
 
I am thinking shared neutral, possible from the time clock motor?
 
Yes, the neutrals were the problem.

Whoever moved 2 of the storage heater points onto the 24hr side only moved the lives, and not the neutrals.
Everything worked as it should, but when I turned off the offpeak mainswitch, the 2 circuits that had been moved no longer had a return path.

So an hours fault finding and switch replacement turned into a 3 hour job.

"it was an electrician that did that!" pronounced the customer.
Yes... the same electrician that didn't mark up the board whatsoever
 
Yes, the neutrals were the problem.

Whoever moved 2 of the storage heater points onto the 24hr side only moved the lives, and not the neutrals.
Everything worked as it should, but when I turned off the offpeak mainswitch, the 2 circuits that had been moved no longer had a return path.

So an hours fault finding and switch replacement turned into a 3 hour job.

"it was an electrician that did that!" pronounced the customer.
Yes... the same electrician that didn't mark up the board whatsoever
Do i get a prize?
 

Reply to Head scratcher for trainees, and others in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
160
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock