A

aes2011

Ok, so I have a surface 2x58 5ft modular fluorescent fitting. Changed both tubes and starters. Each tube has their own ballast. One tube is running fine, however the other one flickers, goes on for around 20 secs then goes off...then the starter keeps on trying to fire up. When I pull the starter out when the tube is lit, it stays lit...

Bemused.
 
The fitting is no more than three years old. I've used the other starter that works fine with other tube and same problem...
 
If you've got a 2 tube fitting with 2 separate ballasts it should be easy enough to just swap parts from one side to the other and figure out which component is causing the problem.

If it's in an awkward location or needs access equipment to get to it I would just replace the complete fitting. Nothing worse than needing to re-erect scaffold for an intermittent problem.
 
as marvo said... be easier and cheaper in long run...! some times ballasts dont last 2 years in lights and cost 3x the cost of the fitting!¬
 
This is a current flow problem, are you using electronic starters or standard (cheap) ones? There is insuficient current flowing to hold the starter in the o/c position, which means, if you have swapped the tubes over, and swapped the starters over, and the fault remains, the ballast is faulty. I have often found that this fault can be caused by loose spring clips on the push in type wiring connections on the fittings, especially at the ballast where it gets hot. modern fittings are CR*P.
 
Sounds like the starter is tired or not the correct value for the size of tube/ballast combination.

"When I pull the starter out when the tube is lit, it stays lit..." this indicates that the ballast is able to limit the current and maintain ionization. So shorted turns on the ballast choke is unlikely.

Most likely then that the RFI suppression capacitor across the starter contacts is breaking-down/leaky bleeding off sufficient current to quench the ionisation.
 
Last edited by a moderator:

Reply to HELP! 2x 58w 5ft fluro fitting fault in the Australia area at ElectriciansForums.net

Similar Threads

T
So I was called again to look at light in unit that has gone off. Of course when I got there it was on (again) The circuit is very straight...
Replies
40
Views
6K
The Ghost
T
I have a small utility room at the end of my garage, it have a fluorescent fitting for lighting controlled by an infra-red sensor. I decided to...
Replies
21
Views
2K
W
Hey, I've been a member for a few years and used this forum occasionally to answer or confirm electrical questions i've had in the past, but this...
Replies
15
Views
6K
S
4ft old style starter/ballast type fitting which when powered does nothing at all (not a flicker) but trips the 6A/30mA RCBO after maybe 3-5 secs...
Replies
9
Views
3K
W
The setup is a detached garage with mains incoming though the wall, goes into main switch and fuse unit. Out comes a wall socket line, and a...
Replies
6
Views
2K
mogga
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock