Bit of a strange one or I'm being stupid (I'll let you decide!) New boiler installed in my house tonight. From the switched spur to boiler 3 core LNE, the boiler to a JB have a 4 core cable (live out, neutral out,earth & return to boiler), from here a 3 core & earth to the programmer (Live Neutral & Return from the stat), from the programmer out to the stat ( switched Live, Neutral & return which is joined in the JB) the problem being when the programmer is powered up the live boiler is on, this is without the CH boost or any setting calling for heat on) I thought it's maybe a faulty programmer as when I take the programmer off there ain't 240 coming back in the return. Any help would be greatly appreciated but I'm thinking it's the programmer?
 
Is the boiler in factory mode in the settings or linked out on the terminal strip where the switched feed/live/return would be?
 
As above I reckon that they haven't removed the factory fitted link between live out and switched live return.
Check the switched live return goes from 0 volts to 230 volts ,and back, as it should.
 
Give the electrician a ring who wired it mate. If it's a new installation then it shouldn't be your problem to sort.
 
Is the boiler in factory mode in the settings or linked out on the terminal strip where the switched feed/live/return would be?

The link has been removed. I thought the drawing was a bit strange though. It shows the drawing for internal programmer say terminals 1 & 2= live out & return(this is where the link was) 3=perm L 4=Neutral but then for the diagram for external stat etc it shows the Live coming from the permanent Live & the return going into 2. Infact here's the link page 30 shows you the internal & external. See drawing 33 & 35 are different??Which one should be followed, could be the problem?

http://www.idealheating.com/downloads/manuals/204626_inst.pdf you

 
Drawing 33 shows the perm live coming from the room stat output. Drawing 35 uses the boiler perm live and only returns the switched live to the correct input of the room stat. Could be that the switched live is connected to the perm live out of the room stat connections, try moving it to the other terminal.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Help! Am I being stupid?!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
SSE,
Last reply from
sjm,
Replies
5
Views
1,236

Advert