Discuss I never install ring circuits, the potential for danger is unacceptable in the UK Electrical Forum area at ElectriciansForums.net

... yes, there is something wrong with ring circuits - as I stated in my post.

Why would you never ever install a tree circuit?
Pointless joints all over the circuit. Poor design. Would much prefer ring or normal radial. As stated, anything is dangerous when interfered with by non competent persons there is absolutely no need to work at a circuit when you don't have a clue what your doing, otherwise they are perfectly acceptable and safe
 
There are pros and cons for any wiring scheme but the humble RFC has a lot going for it. Mainly fault tolerance, if a conductor is broken the worst case is that a single cable might carry 32A, that's about 18.5W/m and only a little more than a complete ring might take on one limb anyway.

As mentioned by others, the same applies to the CPC, a break in the cable leaves some protection intact.

By contrast, a single fault on a radial can be a serious problem. Best case, your kettle doesn't work, intermediate case you lose earth protection, worst case the arc from a cracked conductor burns your house down.

The last one is a common problem in territories that use radials as standard, which has led to the emergence of AFDDs, which sometimes shut off power before the fire starts, sometimes not.

Regardless of why RFCs appeared, they're a robust and simple engineering solution to improve safety, for little extra cost and effort.
 
I’d like to know if anyone else here refuses to install ring circuits in domestic premises.

For me it’s either a 20a radial / tree circuit with 2.5mm, or a 32 radial / tree circuit with 4.0mm.

Frankly I’m tired of finding broken ring circuits on 32a CB’s, as well as mismatches on end to end tests. It drives me nuts on jobs that should be simple.

I wish we would get rid of this ridiculous practice here in the UK.

I know some of you will say there’s nothing wrong with it when it’s properly installed and tested, but inevitably at some point in the future someone will come along and disconnect a conductor unknowingly while changing outlets on the circuit.

Testing is more complicated, and diagnosing faults on a ring also.
 
Same old argument. "Ring circuits are dangerous if someone who has no clue messes with them." Same goes for any circuit.

I find precious few ring final faults and have never seen any substantial evidence that significant danger is posed even when rings have been made discontinuous. Only in theory.

Anything installed properly is safe. Anything installed then messed with has the potential for danger. The argument has no point.
 
I think the OP uses 'tree' to describe an ad-hoc radial with branches but it has a much older, more established meaning. The tree system of wiring was used in the late 1800s and early 1900s as an alternative to the distribution system that we use now (i.e. terminating a main or submain in a DB and distributing circuits from there).

In the tree system, the main would take a shortish, straightish route through the building and wherever a circuit was needed, a local fuse would branch off. Like taps in a riser busbar, but not necessarily in a riser. The main could also taper like the trunk of a tree, as it could be fused down stepwise as branches relieved it of some of the load. Pattresses with one or two pairs of ceramic pepperpot fuses would be dotted around here there and everywhere, resulting in difficulty of isolation and localisation and inflexibility once installed.

The advantage of a tree, in some layouts, was that less wiring and shorter runs were often possible, giving lower drop for the same amount of copper. But the flexibility of the DB method had won out by the 1920s and tree wiring was soon abandoned.
 
When the topic was last aired, I said I would like to see examples of thermal damage to RFC cables caused specifically by overload of one leg, due to the other going O/C. None have been offered so far...
 
Personally I've never come across a RFC that was broken and then overloaded. My opinion is that its not likely to happen in most homes, possibly the kitchen where there is a potential of higher wattage equipment being simultaneously used (which is one good reason to wire a kitchen on its own RFC). Again my personal opinion is that RFC's are less likely to be dangerous should a fault occur, an example, as a few have already mentioned - the continuity of the cpc is more likely to remain intact or at least partially intact for the majority of the circuit.

The only one problem I see with RFC's - The ignorant people who don't understand them.

Sorry O.P but you don't have my vote.
 
Easy fault finding = Making do without a mft , very DIY.
..because it works has not confirmed the "Earth" is any good..
-the proper phrase uses the word "protective"-!
 
A “tree circuit”, the Americans refer to them as a MWBC (Multi Wire Branch Circuit). Most electricians hate them, but they are a throwback to the past.

Another comparison is the UK Octopus wiring system, something I’ve installed myself for lighting but it can be used for power. It’s a good system so long as you have easy access to the central JB, fault finding is easy.

As for RFC’s, I’m in the fellowship of the ring (sorry Mr Tolkien).
 
i wouls say that a "tre" circuit is one where there is a radial off the OCPD, which then branches into several branches, each feeding 1 or 2 outlets. ifthe junction is either MF or accessible, as long as it's installed properly and the feed from the OCPD is rated according to the total load, then it will comply. still not a good departure from a RFC. many a RFC insyakked 50 years AGO WITHOUT SOME NUMPTY MESSING WITH IT, IS STILL FIT FOR CONTINUED USE.

AND... thE bloody caps lock next to the "A", FAT FINGERS. ARRRRGHHH.
 
I've heard it all now

Rings are dangerous lol

I always remember talking to a builder from Hungary who was slating the way we build houses in the UK

He really disliked building control.....

(Edited by staff, please respect forum rules, expletive removed).
 
Last edited by a moderator:
I've heard it all now

Rings are dangerous lol

I always remember talking to a builder from Hungary who was slating the way we build houses in the UK

He really disliked building control.....

(Edited by staff, please respect forum rules, expletive removed).
You should have told him to F Off back home if its so perfect back in Hungary.
 
Just to add another little angle, anyone done 4mm rings where insulation or circuit length is a bit of a concern ? :) I did it in a large kitchen a year or so ago. If anything [with 35mm boxes] I think the stranded 4mm is just as easy to terminate.

Done this many many times, in very large houses it is a necessity..
Also wired many rings where the 1st and last sockets have been 4mm and the rest in 2.5...
Surprised no suckers have mentioned the good old lollipop jobs
 
Here in Spain it is the norm to do Spider wiring !! Each socket goes back to a large box where there is a large Chocolate Block ! (even lighting circuits) This Mickey Mouse system is used around Europe, The U.K. has the BEST system in the world ! I have seen so many Melted sockets here where someone has tried to do a radial (Ryanair sparks?) Ring Circuit, Superior !
 
Here in Spain it is the norm to do Spider wiring !! Each socket goes back to a large box where there is a large Chocolate Block ! (even lighting circuits) This Mickey Mouse system is used around Europe, The U.K. has the BEST system in the world ! I have seen so many Melted sockets here where someone has tried to do a radial (Ryanair sparks?) Ring Circuit, Superior !
Dark or Milk, Chocolate block? Question, what's a Ryanair Sparks?
 
HARD HAT ON

A Ring Final is intrinsically unsafe in that it can be inadvertently, damaged in such a manner as to overload the cable on the undamaged leg.

There is no denying or getting away from this FACT.

They are an anachronism, a stop gap belonging to a bygone era.

The simplest test, and one rings fail, is;-

IF THEY DIDN'T EXIST WOULD THEY BE INTRODUCED TODAY?

No sane person would answer yes.

They offer very little advantage over Radials yet, as stated, are intrinsically unsafe.
 
HARD HAT ON

A Ring Final is intrinsically unsafe in that it can be inadvertently, damaged in such a manner as to overload the cable on the undamaged leg.

There is no denying or getting away from this FACT.

They are an anachronism, a stop gap belonging to a bygone era.

The simplest test, and one rings fail, is;-

IF THEY DIDN'T EXIST WOULD THEY BE INTRODUCED TODAY?

No sane person would answer yes.

They offer very little advantage over Radials yet, as stated, are intrinsically unsafe.
 
HARD HAT ON

A Ring Final is intrinsically unsafe in that it can be inadvertently, damaged in such a manner as to overload the cable on the undamaged leg.

There is no denying or getting away from this FACT.

They are an anachronism, a stop gap belonging to a bygone era.

The simplest test, and one rings fail, is;-

IF THEY DIDN'T EXIST WOULD THEY BE INTRODUCED TODAY?

No sane person would answer yes.

They offer very little advantage over Radials yet, as stated, are intrinsically unsafe.
Especially when lots of people aren't sure on how to test them and if they do know how to interoperate any results.
 
I did but never the cheapo airlines, anyway what's that got to do with my question, trying to win some points?
pete. every time i see one of your posts, reminds me of this title:
 
Especially when lots of people aren't sure on how to test them and if they do know how to interoperate any results.
Sure being able to test one allows us to feel superior.

But it always amazes me that rings are defended with such passion, it's like I've just called their pint a puff.
 
Opinion from a Kiwi.
Found rings to be a bit strange when I started work in Eire. Decided they have their uses especiaĺly for simple installs like a 2 story 3 bed terrace. Anything much bigger they're a pain in the arse. Those fused plugtops are a pain too and so bulky.
My biggest concern tho is how half brained drongo without any training can call themselves a Sharkie and start wiring
 

Reply to I never install ring circuits, the potential for danger is unacceptable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
Hi all. Long time lurker, first time poster. I am not an electrician but I enjoy learning as much as I can. I am currently renovating a house...
Replies
10
Views
1K
The Ghost
T
S
Greetings all, I'm looking for a bit of advice. I'm not actually an electrician, but I am an electrical design engineer and I am aware of the...
Replies
33
Views
3K
Hi guys, I have come across two problems today well acutely three so I will list them first.. 1st Testing a 4mm radial circuit today or so I...
Replies
18
Views
7K
Engineer54
E
D
Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you...
Replies
59
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock