But you can only omit the rcd if it's a like for like swap. If it's not the same rating then it's not like for like.

Which regulation will you be using to support that statement?


Sent from my iPad using Tapatalk
 
Part p of the building regulations.
 
Gents

In relation to an addition or alteration to existing electrical installations.

this thread goes to the heart of the tension between professionals and the domestic consumer which get faced everyday. Part P does, however, still direct us to designing and installing in accordance with BS7671.

Then we we get the bit which says the building should be no more unsatisfactory .... then when the building work was started.

Then we are directed to do any new work according to BS 7671 and we must check the existing installation a) rating and condition for new loads (does not say anything about like for like loads) b) Adequate protective measures are used c) Earthing etc satisfactory.

Then we are given the list of notifiable work, shower room for instance. This bit is important to this discussion, I suggest, as minor additions and alterations are notifiable in this case.

A simple swap, like for like model and rating of shower unit, would ordinarily pass the no more unsatisfactory test, as long as b and c above being satisfied.

Which leads us to BS 7671, if you agree with me so far. Where I suggest if we touch this particular circuit we adopt wiring regs and add an RCD. 701.411.3.6. Uses the word shall, not maybe, might, is optional etc.

cheers
 
  • Like
Reactions: 1 person
As far as I am aware, there is no requirement to notify when replacing equipment, irrespective of whether the equipment is in a special location.

As for the OP's query, it is up to the person conducting the work to comply with the requirements of BS7671.
In this particular instance there is no requirement to provide RCD protection, as the work is replacing equipment.
 
As far as I am aware, there is no requirement to notify when replacing equipment, irrespective of whether the equipment is in a special location.

As for the OP's query, it is up to the person conducting the work to comply with the requirements of BS7671.
In this particular instance there is no requirement to provide RCD protection, as the work is replacing equipment.

But in this instance the equipment been installed comes with a manual and it will say in there that an RCD MUST be installed. No getting around it.
 
  • Like
Reactions: 1 person
And consider the manufacturers installation instructions, which will advise RCD installation. We can always live in past, and install equipment connected to bare wires circa Edwardian times. But safety moves on.
 
  • Like
Reactions: 1 person
It is quite possible that the manufacturer's instructions do specify RCD protection be provided.
Unfortunately, without knowledge of either the manufacturer or their instructions, I am unwilling to offer an opinion as to what such instructions do or do not require.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
is it up to the customer what protective device is in his installation?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
juice,
Last reply from
Deleted member 26818,
Replies
27
Views
3,128

Advert