Sorry to bring up an old post but im confused.
I have carried out tests on a kitchen ring final wired in 2.5mm/1.5mm T&E, results as follows:
r1=0.36 rn=0.34 r2=0.59
I then joined leg 1 of line conductor to leg 2 of cpc and leg 2 of line conductor to leg 1 of cpc and measured the R1+R2 at each socket outlet, the highest reading for R1+R2 = 0.26.
We know that:
1.5mm = 12.10 mOhms/m
2.5mm = 7.41 mOhms/m
12.10 + 7.41 = 19.51
19.51 mOhms/1000 = 0.01951Ohms/metre
therfore R1+R2 / 0.01951 = length in meters
0.26 / 0.01951 = 13.326m
But the cable I have used is about 35 meters?
Could someone please explain my results and offer any advice
Thank you all