Hi all New to the forums but been working in the industry for 10 + Years now have my level 3 and 17th edition. Employers just put me on the inspection and testing course, not sure what to think at this moment on my second day. Initial letter says 5 days but looks like after this week will have to go in for a further two more tests, seems like they throw quite a lot of content your way in such a short amount of time.
I like to think i have had a lot of experience with testing and inspection, done quite a few periodic inspections with 30+ Distribution boards and probably the most experienced in the class but i'm still bricking it!
Was wondering what these qualifications will actually mean for me or allow me to do if anything extra, i don't see what my employer gains from sending me on this course?

P.s. I don't think city and guilds know what they are even talking about sometimes, get this sample question for instance:

Increasing the length of a cable would NOT affect the;

a. Voltage Drop
b.loop impedance
c.rating of the protective device
d.insulation resistance

C&G's correct answer was C announced the tutor! I don't have high hopes for the real life test where i can put in the 100% correct answer only for it to be wrong.
 
C is the correct answer, though... (in theory, anyway). Longer cable increases the VD because V=IR and R will be bigger (more cable). The loop impedance will be bigger for the same reason. And the IR will be lower as you've got more insulation in parallel. How can putting a longer cable in change the rating of your fuse/circuit breaker? So C is your answer.

It is a lot of info to take in over 5 days. If you've been doing it for 10 years, you will be well up to speed on the techniques and practical aspects. What you'll have to get your head around is calling everything by its proper name. It's not a megger, avo, or even a continuity tester: it's a low-resistance ohmmeter.

Read GN3 cover to cover. Then repeat.

Good luck :)
 
Upvote 0
I read the question, and my answer is also c.
The critical word in the question is NOT.
If you increase the length of a cable then a, b and d are all affected.

C&G often word their questions in an obtuse way, so you gotta read it carefully!
 
Upvote 0
C&G often word their questions in an obtuse way, so you gotta read it carefully!
They do! They go on a special technical course on how to set questions in such a way that you can't skim-read them, you have to read them carefully and work out what exactly they're asking.

It's called the "sneaky gits" course, I believe...
 
Upvote 0
Long discussions with the tutor and we have both come to the conclusion that C&G's are sneaky buggers for there wording yes!
 
Upvote 0
D. is the correct answer.

Cable length could be 1m or 200m. It is testing the insulation resistance, not the length of the conductor. The other options are all related to length of conductor!?!?!?!?!?! Although the option are all related, the key word is """NOT"""
 
Upvote 0
Straightforward question, apart from the negative aspect of it. That's there to make you stop and think for a second! :-)
It is clearly C.
Ask yourself why it's not A,B or D.
 
  • Like
Reactions: Leesparkykent
Upvote 0
D. is the correct answer
Nah

If you have a 200metre length of cable, the IR will be more than a 1metre length. Not by much, but it will be more.
 
  • Like
Reactions: Casper
Upvote 0
oh yes, less Megohms. Bloomin' Merlot......:bananas:
 
  • Like
Reactions: Leesparkykent
Upvote 0
Increasing the length of a cable would NOT affect the;

a. Voltage Drop
b.loop impedance
c.rating of the protective device
d.insulation resistance

C. """affects""" the choice of the OPCD due to A & B. Insulation Resistance will not be effected due to the length of the cable!

Time loop impedance "affects" the designed OPCD due to length of the cable run. The answer is still D in my book. (Tin hat on)
 
Upvote 0
Upvote 0
I would say that if the question were saying "if you only increase the length of cable what does not change?"
Then the rating of the protective device would not change as you have not changed it!
The choice of protective device may be altered by the maximum EFLI permitted for that device.
Volt drop increasing may limit your design current, not necessarily the choice of protective device.
Increasing the cable length would increase the surface area of conductors in close proximity and so will reduce the insulation resistance. This is similar to testing one circuit alone vs. testing multiple circuits simultaneously, though the resistances are parallelled in the multiple circuits scenario and so make a larger difference. However for a new cable the result may still be off scale in both cases. C is certainly the C&G answer:confused1:!
 
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
On the dreaded 2394 - 2395 Course
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
16
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Chris Harrison,
Last reply from
Richard Burns,
Replies
16
Views
3,062

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.