Hi,

I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service and since it's come back, items which passed easily last year (Earth Continuity below 0.1ohm), are now not passing. I've now raised the earth continuity limit to factor in cable resistance etc. but why is it that some items which were say 0.8ohm are now 0.17ohm and wont pass? Any ideas?

Many thanks,
 
Because it wasn’t calibrated.

Out of calibration means that something is off inside the machine which can give false readings.
When it goes to be calibrated, these “off” things are adjusted against test examples with known good values…. Which brings the results back to being more accurate.
 
  • Like
Reactions: Rozzerdinho
Because it wasn’t calibrated.

Out of calibration means that something is off inside the machine which can give false readings.
When it goes to be calibrated, these “off” things are adjusted against test examples with known good values…. Which brings the results back to being more accurate.
Hi. We have annual calibration certs since we purchased the machine.
 
  • Like
Reactions: Avo Mk8
0.17 Ohms is less than 0.8 Ohms, so that's a better earth continuity result. Uess I've misunderstood your post.
 
0.17 Ohms is less than 0.8 Ohms, so that's a better earth continuity result. Uess I've misunderstood your post.
Apologies it should say 0.08 and not 0.8.
 
Ah fair enough. Have you got a decent multimeter you could use to verify the results. Vital to get good connections obviously when you're measuring such low resistances.
 
  • Like
Reactions: Rozzerdinho
If you keep your PAT results from previous years, can you review these for evidence there has been a step change in the Apollo results after calibration, if that is what's happened.
e.g. If you have results for workshop equipment that showed a value of around 0.08 ohms year on year for 3 or 4 years, and now the value is 0.17 ohms, and you then look at the results for more equipment, and they have all done the same thing (even better if they are now all around 0.09 ohms higher), then you have solid evidence your Apollo is suddenly producing consistently different results from all previous years, and I would send it back for investigation.

It's not that unusual for equipment to get upset in transit, or less likely for an error to be made during calibration.
If the data gives evidence there's a consistent change in the Apollo's results, the calibration company ought to look into it for you.
 
If you keep your PAT results from previous years, can you review these for evidence there has been a step change in the Apollo results after calibration, if that is what's happened.
e.g. If you have results for workshop equipment that showed a value of around 0.08 ohms year on year for 3 or 4 years, and now the value is 0.17 ohms, and you then look at the results for more equipment, and they have all done the same thing (even better if they are now all around 0.09 ohms higher), then you have solid evidence your Apollo is suddenly producing consistently different results from all previous years, and I would send it back for investigation.

It's not that unusual for equipment to get upset in transit, or less likely for an error to be made during calibration.
If the data gives evidence there's a consistent change in the Apollo's results, the calibration company ought to look into it for you.
Hi Avo,

Thanks for the reply. Think that's what i'll end up doing. The cal cert says everything is fine but i'll get a better picture once start comparing back.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Aberdeen
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
EthosEnergy Light Turbines

Thread Information

Title
PAT Testing fail query
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Rozzerdinho,
Last reply from
Rozzerdinho,
Replies
7
Views
1,570

Advert