Hi All,
Need advise on something.
I have seen a diagrem somewhere showing that we cant have any electrical socket near the washbasin/tub etc. However when visiting my friend's house, which is a new build, I saw that the electric tap for the wash basin had a sicket just below the washbasin. Althought that area was enclosed in a fitted cabinet.
Question: is is ok to have sockets inside a fitted cupboard and within the "no sockets" zone in the bathroom?
 
The zones are for distances from baths and showers.

1643293900094.png

As you see, depending on the distance, there is no zone for a washbasin. Also it is within a cupboard.
Personally I'm not a fan of sticking a socket there. I would have used a switched fused spur and hardwire it in that. Stops idiots plugging other stuff into it.
 
3m from zone 1. if in an enclosed cupboard, then the 3m rule can be ignored.
 
Ieed advise on something.
I have seen a diagrem somewhere showing that we cant have any electrical socket near the washbasin/tub etc. However when visiting my friend's house, which is a new build, I saw that the electric tap for the wash basin had a sicket just below the washbasin. Althought that area was enclosed in a fitted cabinet.
Question: is is ok to have sockets inside a fitted cupboard and within the "no sockets" zone in the bathroom?
i this post from hello hello .🤣🤣
 
I thought the enclosed clause was if it was only accessible using a tool.
Firstly, I want to shake you by the hand as you have unwittingly solved a long standing mystery for me.
Until this evening, I have never managed to see what that * at the bottom of the page was referenced by. I knew the rule from the text earlier, but couldn't ever find any corresponding *'s.
I had clean glasses for once, and was sitting in the best lit chair in the house, and bingo! The two tiny specks leapt out for the first time ever. And by heck they are small! One less mystery in the world.

1643311111366.png

Ok, now that's out of the way. The tool thing is only relevant if the area in question is in zone 0, promoting it to zone 1.
There are no zones specifically relating to a wash basin (don't be confused by the hundreds of diagrams on the web showing a zone around a basin, they are all wrong!).
e.g. THIS IS WRONG:
1643311818544.png
So forget that bit completely.

Normally sockets are permitted 3m from zone 1, but the cupboard counts as a fixed partition (see 701.32.1 General) so is out of zones even if the room is small that the wash basin is within 3m of zone 1.
 
Firstly, I want to shake you by the hand as you have unwittingly solved a long standing mystery for me.
Until this evening, I have never managed to see what that * at the bottom of the page was referenced by. I knew the rule from the text earlier, but couldn't ever find any corresponding *'s.
I had clean glasses for once, and was sitting in the best lit chair in the house, and bingo! The two tiny specks leapt out for the first time ever. And by heck they are small! One less mystery in the world.

View attachment 94375

Ok, now that's out of the way. The tool thing is only relevant if the area in question is in zone 0, promoting it to zone 1.
There are no zones specifically relating to a wash basin (don't be confused by the hundreds of diagrams on the web showing a zone around a basin, they are all wrong!).
e.g. THIS IS WRONG:
View attachment 94377
So forget that bit completely.

Normally sockets are permitted 3m from zone 1, but the cupboard counts as a fixed partition (see 701.32.1 General) so is out of zones even if the room is small that the wash basin is within 3m of zone 1.
Thanks, I was lacking the enthusiasm to pick up the regs tonight. It's not just out of zones but out of location according to that paragraph. I do wonder if that was the intent. It's logical for a boiler in a cupboard but a bit odd of a socket.
 

Reply to Power socket in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
2K
I'm about to do wiring for a small apartment in Azerbaijan. Mostly I will try to use UK standards - ring mains with ELCBs, everywhere earthed, T&E...
Replies
10
Views
3K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
791
Good afternoon I have recently had a bathroom makeover and had the existing shaver socket removed as I purchased a cabinet with socket enclosed...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock