Hi,I am on a job and at the moment there is a 10mm T&E powering a sub board in a flat downstairs, I am rewiring the whole house but this is the 1st time ive come across this, the Ze at the main board is 0.30 and im allowed 0.35, what size and type of cable would you run, a couple of the guys at work are saying 25mm 3 core swa, do you think this will be the case, im going to be powering this sub board from a 100A switch fused from a phase block, any suggestions would be much appreciated,

Many Thanks
 
16mm with a 80A switch fuse should be adequate for a flat.
 
  • Like
Reactions: 1 person
Hi, Thanks for the replies, I have already bought a 100a switch, will 16mm still be ok for this?

Many Thanks
 
What size is the incoming cut-out fuse? 100A max. Down rate the fuse in the switch to 60A and use 16mm. A flat doesn’t take that much even if a shower is fitted.

I’ll bet I could run my flat off a 16A fuse.
 

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Powering Sub Board
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
allybally,
Last reply from
Knobhead,
Replies
4
Views
1,416

Advert