What a chuckle,just read this months P E magazine and there,s a cracker in the faults section,a photo of a switched fused spur wired in 2.5 straight into a set of henly blocks with the tails! No wait thats not the funny part,the laugh is the so called electrician who states that "it was my mates house and there was 100 amp going through a 2.5 feeding garden lights,and it had a 13a fuse in the fcu.Obviously a classic case of someone without a clue,just because it,s connected to the henly,s and therefore protected only by the 100a? service fuse doesnt mean its taking 100a, and if it was they,d be big outside lights and what about the 13a fuse? Just proves worryingly how little knowledge some people have.
 
Its a change though from the usual "there's X amounts of volts flowing through it"
Perhaps there is X amount of volts flowing through it with that 100 amp current as well :mad2:
 
  • Like
Reactions: 1 person
What a chuckle,just read this months P E magazine and there,s a cracker in the faults section,a photo of a switched fused spur wired in 2.5 straight into a set of henly blocks with the tails! No wait thats not the funny part,the laugh is the so called electrician who states that "it was my mates house and there was 100 amp going through a 2.5 feeding garden lights,and it had a 13a fuse in the fcu.Obviously a classic case of someone without a clue,just because it,s connected to the henly,s and therefore protected only by the 100a? service fuse doesnt mean its taking 100a, and if it was they,d be big outside lights and what about the 13a fuse? Just proves worryingly how little knowledge some people have.
yep...seen it phil.....theres another belter (quite literally ) n all....just take a look at the right hand page of `caught on camera`...now, in the top left of the right hand page check out the pic of the joints on them tails WITHOUT any enclosure of any kind....hmm...definately the worst of this months nastys in my op....
 
Phil i've seen a 10mm cable 3 phase supply coming off of a Bus chamber that had 1200amp fuses protecting it .................... granted the 10mm was feeding a 32amp TP+N switch isolator for a battery charger.

When I asked as the know it all apprentice about 10mm on 1200amp fuses .was told by the sparks.

"Well was going to use some 6mm but could not find lugs big enough to bolt onto the bus, hate over specing the job"
 
  • Like
Reactions: 1 person
the one with the genny though will never cease to crease me though....an `earth rod in a bucket of sand?`....
 
  • Like
Reactions: 3 people
Phil i've seen a 10mm cable 3 phase supply coming off of a Bus chamber that had 1200amp fuses protecting it .................... granted the 10mm was feeding a 32amp TP+N switch isolator for a battery charger.

When I asked as the know it all apprentice about 10mm on 1200amp fuses .was told by the sparks.

"Well was going to use some 6mm but could not find lugs big enough to bolt onto the bus, hate over specing the job"
well...you can fuse either end Malcolm......as long as the demand doesn`t exceed the Iz of the cable....
 
  • Like
Reactions: 1 person
yep...seen it phil.....theres another belter (quite literally ) n all....just take a look at the right hand page of `caught on camera`...now, in the top left of the right hand page check out the pic of the joints on them tails WITHOUT any enclosure of any kind....hmm...definately the worst of this months nastys in my op....
Yep spotted the fault straight away,should have rcd to protect against direct contact lol,seems that bodgit and scarper really are uk wide after all.:joker:
 
  • Like
Reactions: 1 person
well as far as i can see the worst aspect of the `install`...that Phil has pointed out is the lack of a means of isolation...
 
Well certainly for fault protection yes G it should be that.

Overload is slightly different as in reg 433.3.1 (i) and (ii) and the fixed load
 
I don't think the forum should be giving the impression, to those that don't know any better, that 2.5mm T&E on a 100A fuse is a good idea. Fair enough, overload protection may be omitted on account of the 13A maximum loading, but under short circuit conditions there's every likely-hood that the 1.5mm cpc will be vaporised. 543.1.3 applies...
 
I don't think the forum should be giving the impression, to those that don't know any better, that 2.5mm T&E on a 100A fuse is a good idea. Fair enough, overload protection may be omitted on account of the 13A maximum loading, but under short circuit conditions there's every likely-hood that the 1.5mm cpc will be vaporised. 543.1.3 applies...
lExactly,the point I was making was that a so called spark who posted it in the magazine ignored the blindingly obvious issues and seemed obsessed with the mistaken belief that because the FCU was connected directly to a 100 amp service fuse then it was drawing 100 amps.Rather than actually understanding that the 100amps is what is available but only the current required by the item in use is what it taken,in the case of a few outside lights probably less than 2 amps.
 
lExactly,the point I was making was that a so called spark who posted it in the magazine ignored the blindingly obvious issues and seemed obsessed with the mistaken belief that because the FCU was connected directly to a 100 amp service fuse then it was drawing 100 amps.Rather than actually understanding that the 100amps is what is available but only the current required by the item in use is what it taken,in the case of a few outside lights probably less than 2 amps.

Read it yesterday.

Best bit is that this cable runs so hot that in the winter its the only cable running outside with no snow or ice on it. The other one that made me also chuckle is the letter titled 'garage nightmare'.

How the hell do they know theres no RCD inside the house and the bit about the cleat being upside down. Personally, I never knew there was a right way for any kind of cable clip.

Think they should change the magazine title to, Professional Electrician and DIY Enthusiast
 
Read it yesterday.

Best bit is that this cable runs so hot that in the winter its the only cable running outside with no snow or ice on it. The other one that made me also chuckle is the letter titled 'garage nightmare'.

How the hell do they know theres no RCD inside the house and the bit about the cleat being upside down. Personally, I never knew there was a right way for any kind of cable clip.

Think they should change the magazine title to, Professional Electrician and DIY Enthusiast

I think the problem is that we now have so many so-called "professional electricians" with absolutely no training or experience other than that which a test bench at college gives them, so they may as well be DIY enthusiasts.
 
Amp David;59816 and the bit about the cleat being upside down. Personally said:
Might just have been my mentor's personal preference but he told me that the nail or screw on a clip or cleat always went on the bottom wherever possible as that's what's bearing the weight of the cable. I have continued this level of ---- retentiveness to this day:)
 
  • Like
Reactions: 5 people
That's my point trev, what right and whats wrong.

Horizontal run I always fix from the top with cleats and the bottom with clips and when vertical from the left.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Professional electrician ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
Guest111,
Last reply from
mountainman,
Replies
20
Views
2,959

Advert