Hello,

I've never had this before so sorry for sounding silly...

I did a re-wire for a customer the other week, now they have decided they would like an outside socket.

Every things been tested, there's a spare way left on board so all I need to do is run a new circuit but what cert would I need to do for this? or would I need to re-test the whole board?

Thanks,
Carl
 
if it's a new circuit you need to fill out a EIC.for that 1 circuit. can you not add it to the scedule of test results. if you can come off an existing circuit, you only need a MWC.
 
Last edited:
if you can come off an existing circuit, you only need a MWC.

That would be to easy hehe, I was going to do that but it's going to easier just do run new circuit because of location etc.

So I can just test that one circuit and leave all the other circuits alone and just issue a separate EIC for that one circuit.

Thanks, never had to come across this before.
 
That would be to easy hehe, I was going to do that but it's going to easier just do run new circuit because of location etc.

So I can just test that one circuit and leave all the other circuits alone and just issue a separate EIC for that one circuit.

Thanks, never had to come across this before.

as the rewire was only recently done, i would just add the new circuit to the schedule of test results on the rewire EIC.
 
Hello,

I've never had this before so sorry for sounding silly...

I did a re-wire for a customer the other week, now they have decided they would like an outside socket.

Every things been tested, there's a spare way left on board so all I need to do is run a new circuit but what cert would I need to do for this? or would I need to re-test the whole board?

Thanks,
Carl
Isn't this job notifiable?
 

Reply to Re-wire done other week, now require extra circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
682
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
441
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
276
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
813

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock