Hoping to install (if things get back to normalish) a Ryefield board on a job soon. Haven’t installed one before, according to the drawing from UKPN, the meters will be after the ryefield board - will the suppliers do their own tails into the ryefield board or will I have to supply that? Seems a bit of a grey area..
 
The DNO will give you a head and then that is it. Once the installation is complete then you can apply the the meters. All the Ryfield Board and sub-mains must be carried out by the electrical contractor.
 
The dno will request an isolator before the ryefield aswell, also there will be a pme link inside the ryefield (factory fitted ) this needs to be removed if there is to be pme at the head.
 
20200113_173436.jpg
Not the best picture, its installed in a dark basement with other scruffy services but anyway heres one I'm working on. The small enclosure above the Ryfield houses a SPD. Which is fused from the Ryfield unit. I'm going to add an indicator light to the passive relay on the SPD before its finished..
[automerge]1586209405[/automerge]
@sponge23
Check out page 14 for trunking and tail sizes.
 

Attachments

  • UKPowerNetworks_Site-Information-Pack_V2Dec2017_FINAL.pdf
    4 MB · Views: 28
Last edited:
View attachment 57099
Not the best picture, its installed in a dark basement with other scruffy services but anyway heres one I'm working on. The small enclosure above the Ryfield houses a SPD. Which is fused from the Ryfield unit. I'm going to add an indicator light to the passive relay on the SPD before its finished..
[automerge]1586209405[/automerge]
@sponge23
Check out page 14 for trunking and tail sizes.
Thanks mate. Nice neat job that!
 

Reply to Ryefield board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
863
If there isn't a 2-pole isolator there already, I usually get the client to arrange to get one fitted before I do a board change, either through...
Replies
20
Views
3K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock