Steve D

Hi All,

Over the last few years I've been harping on to my company bosses that we need to wise up with our safe isolation procedure.

The company I work for has approx 100 field service engineers, and in the last couple of weeks our training manager has agreed to purchase approved GS38 voltage indicators and proving units for each engineer.
This is instead of using multimeters to test for dead, as they are currently (although, to be honest, I'd be surprised if as much as half our engineers truly did test for dead before working anyway).

However, the proving unit that has been selected is the cheaper 240V type and not the 690V version.
Our engineers do work on 3ph equipment.

The training manager says that his intention is to test from each line to neutral and each line to earth, to check for dead, instead of also testing between lines.

Now, at college, it was always drummed in to us that safe isolation on a 3ph installation is a 10 point test as you MUST test between lines.

Is there a scenario that might arise where all L-N and L-E show dead but there is still a dangerous voltage between lines ?

I'm not really comfortable agreeing to it as is contradicts everything that I have been taught.

What are your thoughts about it ?

Cheers
Steve
 
voltage is also known as potential difference. So if a phase shorted to your CPC/bonding conductor or neutral or both, and you measured between phase and that, then your meter would read 0v. thats why you test between lines/phases.
 
When I carryout checks to prove that a peice of 3 phase equipment is dead consists of 12 checks

Use proving unit to make sure test lamp is working OK then

L1-L2
L1-L3
L2-L3
L1-N
L2-N
L3-N
L1- EARTH
L2-EARTH
L3- EARTH
N-EARTH

Then check test lamp again with proving ubit
 
You should always test across phases as well as there is a much higher PD across phases ie 400V (sqrt(3)x230).
 
I agree Lenny, I personally have got one of the 690v proving units, however my training manager seems content to give everyone the cheaper 240v proving unit.
 
You could argue that if your voltage tester is showing the 240v generated by the cheaper proving unit then that's good enough to tell you that your tester will indicate if voltage is present on your system.
 

Similar threads

F
Replies
0
Views
103
Electricians Jobs
findajob.dwp.gov.uk
F

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Safe Isolation Procedure
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
Steve D,
Last reply from
JulianC,
Replies
6
Views
36,747

Advert