Hi, I am reviewing the calculations for a 200A line with two 3 core 70 sq mm armoured cables, i.e. 2 cables per phase. These cables supplies to a 110KW pump and are installed direct buried along a trench with other 48 power cables in the form of 6 rows of 8 cables each row.

The cables have overheating and losing insulation resistivity. The calculations made had considered 5 cables installed on same row only. I understand this is wrong because there are 8 cables each row and should be applied ather rating factor for each layer. The installer, who made the cable sizing, says that overheating is produced by unbalanced currents on armour.

I have looking for references from BS 5467 standard trying to find the correct rating factors but I did not found anything by the moment. I appreciate if anybody have more information about this issue.

Regards
 
There should be no current flowing in the armour, so long as the current flow in the two cables is the same. To check for circulating currents put a clamp meter around each individual cable, if you have one that can show 3[SUP]rd[/SUP] and 5[SUP]th[/SUP] harmonics then you may find some but unlikely.

As an after thought just make sure that each phase is going down each cable, I found a dual feed to a motor that the contractor had wired with:
Phase A connected to cores 1&2 in cable A
Phase B connected to cores 3&3 in cables A&B
Phase C connected to cores 1&2 in cable B
“It was easier to connect up” the cables were roasting!
 
Last edited by a moderator:
Dojedah,

Are you referring to the number of cables or the number of circuits?? You should only be interested in number of circuits mate!!! Don't forget you are using two 3 core cables as ''ONE'' cable. So are you sure that maybe some of these other circuit(s) are not derived in the same way ??

As so many of these cable over heating problems these days, stems from the use of ''inverter'' controllers... I have to ask, .... do you have such controllers in your installation???
 
Thanks,

Armour is connected in both ends, I have thought that may be better to connect it in one end only


About harmonics, I think is unlikely. The plant have 6 MCC with a dedicated 1,5 MVA transformer each one, and from each MCC there are four 150KW and four 18,5KW VFDs. The VFDs are ACS model of ABB with harmonic filters. II have not checked the motor connections yet, but I have to do it.

Engineer54, number of cables or number of circuits is anything that I do not have clear. The starting system is S-D and the current capacity was calculated for one cable. For this reason I think should be considered the number of cables and not the number of circuits.

In this moment we are planning to install unarmoured cables inside pipes.
 
Thanks,

Armour is connected in both ends, I have thought that may be better to connect it in one end only


About harmonics, I think is unlikely. The plant have 6 MCC with a dedicated 1,5 MVA transformer each one, and from each MCC there are four 150KW and four 18,5KW VFDs. The VFDs are ACS model of ABB with harmonic filters. II have not checked the motor connections yet, but I have to do it.

Engineer54, number of cables or number of circuits is anything that I do not have clear. The starting system is S-D and the current capacity was calculated for one cable. For this reason I think should be considered the number of cables and not the number of circuits.

In this moment we are planning to install unarmoured cables inside pipes.


I don't quite understand your reasoning dojedah??? What has anything you have told us about MCC panels and dedicated 1.5MA TXs got to do with anything?? What's far more important in that paragraph is that you haven't checked any of the motor and other related connections!!!!

Wrong!!! You are using 2 identical multi core cables supplying a load.... doesn't matter a jot what the calculated load or measured load is ...you are using 2 parallel cables as your means of supply. Which to anyone is ONE circuit NOT two circuits. The current is being Shared between the two paralleled cables, for gods sake!!! How the hell did you come up with the idea that you count cables and not circuits, ..even when you know they are paralleled cables???

Well i hope the cables on load side of those VFDs etc are suitably sized and are substantially screened, ....or your going to end up in just the same amount of mess as you are now!!!
 
Pretty sure that ABB recommend an earth cable is run out to the drive along with the cables from their VSD. One we installed recently was fed by 3c 240mm cable and an additional 240mm earth cable run along with it. Check their documentation.
 
Dojedar, in your first post you didn’t mention the cables were for a star/delta motor, setting people off on the wrong track. Have you checked the actual loading on each cable core? In fact what tests have you done? You say the cable IR is failing, to what extent? Give all the information you have and we may be able to help.

As to replacing the cables, that seems to be the knee jerk reaction of someone that’s out of their depth.

2 X 70mm are well on top of the job so there’s a fundamental problem somewhere.

Information needed:
  • Cable IR readings. Original readings as well if you have them.
  • Cable CR readings.
  • Motor IR & CR readings.
  • Ph – Ph voltages while running at both the motor terminals and the starter incoming.
Replacing cables is an expensive option when you don’t know what the fault is yet!

Are any of the other 150KW drives showing the same symptoms? If not then cable replacement is not the answer. To be honest with you with the 1.5MVA supply I can't understand the use of star/delta, the transformers would handle DOL with no problems.
 
Last edited by a moderator:
Dojedar, in your first post you didn’t mention the cables were for a star/delta motor, setting people off on the wrong track. Have you checked the actual loading on each cable core? In fact what tests have you done? You say the cable IR is failing, to what extent? Give all the information you have and we may be able to help.
sorry for the error, was my mistake do not mention the S-D system. The loadings on each core were very similars about 191, 188, 189 A. I say that IR is failing becouse it was measured and values are coming down about 430, 398, 760MOhm each Ph-Gr, and 305MOhm 3Ph-Gr.


As to replacing the cables, that seems to be the knee jerk reaction of someone that’s out of their depth. May be, I just got to plant, the before electrical engineer left the work, there are missing information, if pumps goes shutdown the plant stops and is imperative the plant production, so I have to avoid to stop the plant production at any cost while I am looking for the cause

2 X 70mm are well on top of the job so there’s a fundamental problem somewhere. I'm not sure, 48 power cables direct buried on same trench, in midle east... the calculations made for design shows a current capacity of 112A for each 70 sq mm cable and current demand is 110A, i.e. any small variation on derating factors and it would be undersized, derating factor for 5 cables on same trench is correct?!...spacing between cables considered on calculations is lower than the one showed on trench layout, etc.

Information needed:
  • Cable IR readings. Original readings as well if you have them.
  • Cable CR readings.
  • Motor IR & CR readings. Were made before my arrival and it seems that were good
  • Ph – Ph voltages while running at both the motor terminals and the starter incoming. Pending
Replacing cables is an expensive option when you don’t know what the fault is yet!

Are any of the other 150KW drives showing the same symptoms? If not then cable replacement is not the answer. To be honest with you with the 1.5MVA supply I can't understand the use of star/delta, the transformers would handle DOL with no problems. The power cables that supplies VFD panels have the same symptoms as all the cables that goes by the same trench (other pumps, instrumentation). In addition there are many water overflows over the trench that increases the problem. I would not have use S-D, but I would had used soft starters. The current peaks of DOL affects the other equipment conneted to same transformer.

Thanks for the answer
 
hi there

think plumber

just a passing thought is the mechanical seal on the pump motor a sealed on or does it require greasing could expalin hi currents if not correctly lubricated

cheers
maddfridge
 
Last edited by a moderator:

Reply to SWA Cable Overheating in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
601
Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the...
Replies
6
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
Replies
10
Views
4K
Hi All, I bought a 6mm SWA cable from CEF and realised the external diameter is 15.1mm however on the website it says the external diameter is...
Replies
31
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock