very limited testing of dc
turned up at job this morning a field of solar panels to test
5 mins instructions off we went
carried out irpos to earth array
neg to earth array
polarity
isc with test isolat
voc
managed to test 1 string pair on 50 invertors
not bad for first day!
question - when you say you tested them, do you mean you put the tester on and wrote down the results, or did you also double check that the results made sense in terms of what you'd expect for that many panels on a string in that level of irradiance / temperature?
or was someone else doing that last bit?
yes put tester on and wrote down results, irradiance is being carried out at later time as only 1 meter, each string had its own sheet to fill in results,he needed 25% of each inverter string tested as had a deadline to meet as connecting up tom.
there are 250+ invertors with 4 pairs each and this is just phase 1
learned quite a bit,just been thrown into it really as guy was crying out for help
everything goes back to the guys running it to check results but generally we were looking for reverse polarity, poor ir readings etc
also had to make off sunclick connectors(maybe wrong name)
Reply to testing dc cables in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...