RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

047.jpg

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.
 
Not had much to do with hot tubs neither. Not many people up here have even herd of a bath, let alone a hot tub. But it sounds ok to me. Just be carefull with the frdge/freezer on the rcbo, if it trips and they dont know until a few days later, all the beer and food for the bbq will be ruined.

P.s. You have big thumbs!!!!!!!


Jay
 
hmm. as the cables to the fridge/freezer socket are surface.i could leave on MCB and label as dedicated socket, then a RCD FCU for the hot tub. might have to fit a RCD socket for tool use though.
 
it's not that big. you know how these wide angle lenses distort--- make guys look like they got huge noses? well it's the same.
 
With my Sherlock Holmes hat on,I would deduce you are left handed

"Where are the nicotine stains on the right hand Watson"
wrong on both counts, sherlock. i'm right handed, and don't suffer from nicotine stains, only on my facial hair.

and i use that thumbnail for tightening roofing bolts.
 
it's not that big. you know how these wide angle lenses distort--- make guys look like they got huge noses? well it's the same.


I dont need any help from wide angle lenses to make my nose look big. My 9 year old says it looks like the slope at Xcape in Castleford. I do however need a wide angle lense for something else.........or so the wife tells me...lol


Jay
 
I wonder if anyone can help me..? I have installed a new RCD board in a house that has wiring system of different ages (the guy was strongly opposed on the idea of a full rewire) the previous board being a random assortment of big old fused isolators for each circuit under his stairs. All the circuits held fine apart from the 3 rings. One of the legs for downstairs ring was wired in steel, could this cause a trip? Or am I likely looking for earth faults not picked up by his previous medieval protection?

New to this so apologies if this is in the wrong place, and thanks in advance for any help...
 
You should have carried out an EICR before replacing the CU mate. This would have identified any faults beforehand.
When you say wired in steel what do you mean by that?
What test results were obtained for the RFCs?
 
a new RCD board in a house that has wiring system of different ages



The only correlation between them that I can see, both the wiring system and tels big toe, both are ancient
 
I wonder if anyone can help me..? I have installed a new RCD board in a house that has wiring system of different ages (the guy was strongly opposed on the idea of a full rewire) the previous board being a random assortment of big old fused isolators for each circuit under his stairs. All the circuits held fine apart from the 3 rings. One of the legs for downstairs ring was wired in steel, could this cause a trip? Or am I likely looking for earth faults not picked up by his previous medieval protection?

New to this so apologies if this is in the wrong place, and thanks in advance for any help...

You would be better off starting a new thread for this one. Btw, are you an electrician?
 
Steel instead of copper in the t&e, I know now I probably should have tested first and to be honest I agreed to do the job as a favour for a friend and I'm starting to regret it, and yes I am an electrician I have spent my seven years on new build schools so my domestic fault finding ability is non existent.
 
Fault finding in cables is fault finding in cables no matter where you carry it out mate, a methodical approach is all thats needed.
Steel T&E is something I have never seen in 29 years since I qualified, are you absolutely sure about that?
Once again, what test results did you get from your RFCs?
 
@ OP. try a magnet on the cable. bet it's tinned copper or alli. then you need to IR test each circuit, check for crossed/shared neutrals. and most important, make sure you've not crossed neutrals into wron bar in CU and check manufacturers tails. they have been known to be wired wrong in the sweat shop. (sorry, far eastern technology factory)
 
Just out of interest Sam, what tests did you carry out during your CU change? Have you notified it? What certification did you issue?
What tester are you using?
 
RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

View attachment 12828

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.

13A sounds a bit low for a hot tub all the tubs I've worked on have been 20A - 30A supply to cope with the heater(s) and the pumps. Have you checked the supply requirements of the tub as given the poor original install I would not take anything for granted
 
thought that at first, but it has been running on a 13A 1362 quite happily before the cable failed.
 
RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

View attachment 12828

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.


Hi Telectrix,

I wired a hot tub not too long ago and went by the supplier spec.
They requested a C type 20A mcb, due to start up surge. Also, i wired the supply from the C type mcb in 2.5 swa, into an isolator which also had a commando socket outlet. The company then hooked up the hot tub from their end into the commando socket.

If you do put an RCBO, make sure its C type, as you may have problems on start up.

Hope this helps,
Sav
 
thanks for that. reminded me i've got a 16A type C RCBO in stock. been in the spares box for ages. that'll save a few bob.
 
thought that at first, but it has been running on a 13A 1362 quite happily before the cable failed.

A 13A fuse will carry more than 13A for quite a while before it blows

Hi Telectrix,

I wired a hot tub not too long ago and went by the supplier spec.
They requested a C type 20A mcb, due to start up surge. Also, i wired the supply from the C type mcb in 2.5 swa, into an isolator which also had a commando socket outlet. The company then hooked up the hot tub from their end into the commando socket.

If you do put an RCBO, make sure its C type, as you may have problems on start up.

Must admit never found the need to use C type breakers on a hot tub
 
trhis afternoon it was pi$$ing down so was not a nice job to check the hot tub rating. rest assured that i will check this before making a final decision on OCPDs.( if the rain ever stops). i know i'll need to install 2.5mm SWA just to be within limits on volt drop,
 
Just for my 2 pennies worth, I've only installed 1 hot tub and needed a 32 a supply. Because of the volt drop I had to put in 10mm cable!
I'm sure they are all different, it's quite a varied market and not exactly a day to day job
 
Steel instead of copper in the t&e, I know now I probably should have tested first and to be honest I agreed to do the job as a favour for a friend and I'm starting to regret it, and yes I am an electrician I have spent my seven years on new build schools so my domestic fault finding ability is non existent.

There are electricians and Electricians. I asked, because the terminology you are using does not sound like someone who has undergone any formal training. My wife is not an electrician, but she knows that you do not get steel in T&E....
 
There are electricians and Electricians. I asked, because the terminology you are using does not sound like someone who has undergone any formal training. My wife is not an electrician, but she knows that you do not get steel in T&E....
I think we've scared him off with all this talk of technical stuff like EICRs and testing. I'm thinking he's a DIYer:)
 
What is the hot tub sitting on Tel, ...hopefully not on bare ground or grass?? lol!!
When it stops raining, (..lol!!) check the integral control panel, as most modern hot tubs and Jacuzzis incorporate their own RCD protection.

Personally i wouldn't connect a PME/TNC-S earth to a a hot tub etc that's sitting on concrete, bare ground, grass or tiled concrete base/patio. In such cases go for an earth rod. I think as someone pointed out on another recent thread, that the Reg's call for a local 20 ohm (or lower)) Ra rod to be connected to a PME supplied hot tub/jacuzzi, but i wouldn't recommend that, especially as the users will be walking around with wet and bare feet!!

With TN-S i wouldn't be too bothered, but still prefer to see these tubs sitting on a sturdy built treated hard wooden base and surround...
 
What is the hot tub sitting on Tel, ...hopefully not on bare ground or grass?? lol!!
When it stops raining, (..lol!!) check the integral control panel, as most modern hot tubs and Jacuzzis incorporate their own RCD protection.

Personally i wouldn't connect a PME/TNC-S earth to a a hot tub etc that's sitting on concrete, bare ground, grass or tiled concrete base/patio. In such cases go for an earth rod. I think as someone pointed out on another recent thread, that the Reg's call for a local 20 ohm (or lower)) Ra rod to be connected to a PME supplied hot tub/jacuzzi, but i wouldn't recommend that, especially as the users will be walking around with wet and bare feet!!

With TN-S i wouldn't be too bothered, but still prefer to see these tubs sitting on a sturdy built treated hard wooden base and surround...

funny, was just thinking about earthing arrangement. it's TNC-S and the hot tub is mounted on wooden decking. from what i saw , there is no integral RCD protection. that came from the plug-on power breaker in the pic. would you recommend using the PME earthing ( as it was ) but banging in a rod at the hot tub as well?

i've read through section 702 as being the nearest reg. reference ( swimming pools and other basins) . can't find any reference in the bgb to hot tubs per se.
 
I think we've scared him off with all this talk of technical stuff like EICRs and testing. I'm thinking he's a DIYer:)
Well...yes, someone comes here politely asking for a bit of advice and gets bombarded with interrogation and accusations by the usual do gooder, electrical police types. Why should someone who's only ever worked on new builds know what cable was made out of in the 50's. Its not as if they teach it at college.
 
I dont know if you looked at this post Tel.

hot tubs

just read through it. at the end of the day, my remit is to replace a damaged SWA. but in the process, comply with current regs. and make as safe as possible. also , i'm not happy with the supply being fed from the 1 RCD in the split board in the house, as a fault on the hot tub or in the garage will knock out all the house socket circuits. i need a closer look at the tub ( rating, mounting, any extraneous parts, etc., before finalizing the job.
 
funny, was just thinking about earthing arrangement. it's TNC-S and the hot tub is mounted on wooden decking. from what i saw , there is no integral RCD protection. that came from the plug-on power breaker in the pic. would you recommend using the PME earthing ( as it was ) but banging in a rod at the hot tub as well?

i've read through section 702 as being the nearest reg. reference ( swimming pools and other basins) . can't find any reference in the bgb to hot tubs per se.
Any chance of getting the manuf instructions Tel? They often stipulate installing a rod at the tub end.
 
no instructions. client inherited tub when they bought the house. as i said earlier, it was bucketing down yestrday, so will have to go back and check rating etc., but as it has been running in a 13A plug-in for the last 7 years or so, i am working on the basis that it's no more than 3kW.
 
Sorry i got it wrong, it was GN7 that was being quoted!! lol!!
But even here, it's still not clear what rules/reg's an external hot tub/jacuzzi fall under.... Taking a wild stab, i'd say they have more in common with an outdoor swimming pool than other basin's... lol!!

quote_icon.png
Originally Posted by spark 68
Just out of interest, what does a Jaccuzi fall under ?, would it be under swimming pools and other basins ?, or just under normal bathroom regs ?

A look though GN7 suggests you can use PME for swimming pools and other basins (Zone 2), but with a requirement to have an earthmat or earth electrode 20 ohms or less to be installed and connected to the protective equipotential conductor. 702.410.3.4.3


As far as manufacturers instructions go, you could always try the companies website, they may just have PDF files for their equipment. Or even contact them direct for guidance...



 
Well...yes, someone comes here politely asking for a bit of advice and gets bombarded with interrogation and accusations by the usual do gooder, electrical police types. Why should someone who's only ever worked on new builds know what cable was made out of in the 50's. Its not as if they teach it at college.

He might have been working on new builds for a long time. Does'nt seem like it though.
Anyone who thinks we were ever using steel as a cable conductor in house wiring has to come under a great deal of suspicion. May be polite, may also be very inexperienced.

Basics:mickey:
 
He might have been working on new builds for a long time. Does'nt seem like it though.
Anyone who thinks we were ever using steel as a cable conductor in house wiring has to come under a great deal of suspicion. May be polite, may also be very inexperienced.

Basics:mickey:

I was thinking the same myself
 

Reply to today's fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
767
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock