Piratepete

Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
 
Why not put a 3 gang module away from the steel splash back and feed the sockets from there
 
get him to fit castors to the machines so he can drag them out to isolate.:mad:
 
Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
Yes that’s very helpful – why not reply to Piratepete post more obliging, rather than being silly!
There you go Tel consider yourself severely chastised lol
 
Yeh watch out Tel - Tinks been here for 12 posts - BACK IN YOUR BASKET!
adolph hitler tried . nobody else has come close. my mam was pregnant and was hit by one of them V1 flying bombs. went straight in 1 ear and out the other.
 
The 4mm shouldn't be overloaded if clipped direct, it can handle 37A, and I assume the OCPD is a 32A breaker. However, it would overload the point of the ring where this 'branch' originates from, hence why I wouldn't do it. Just extend the ring and forget about isolators!
 
Not likely to be used at once I wouldn't have thought.

And the each will have their own power use pattern, so you'd need to be unlucky to get all 3 running and running their max current at same time.

FWIW at mine it turns out kitchen and utility room was wired on one RFC and it supports kettle, toaster, micro, dishwasher, washer, dryer and a big fridge. I've not said anything to family and they just get on and jam. I did confirm it is a proper ring and the mcb is not cooked, yet :)
 
And the each will have their own power use pattern, so you'd need to be unlucky to get all 3 running and running their max current at same time.

FWIW at mine it turns out kitchen and utility room was wired on one RFC and it supports kettle, toaster, micro, dishwasher, washer, dryer and a big fridge. I've not said anything to family and they just get on and jam. I did confirm it is a proper ring and the mcb is not cooked, yet :)
we got all that (except for washer/dryer) plus half the downstairs sockets all on a 16A MCB radial. never tripped except when a vivarium heat lamp blew and took out the MCB.
 
I can't find a 7671 regulation and my IET builders guide says if the appliance can be pulled out then the plug and switch behind is ok. So common sense applies ? (not make life tough :))
 
For the area under the bath to be outside zone 1 it must be "only accessible with a tool" (701.32.3). So this means if I don't have to use a tool to get to something, then perhaps it's accessible. Clearly a gorilla could get access to pretty much whatever it wanted :)
 
I wouldn't say a socket behind a washing machine, assuming it is not built in is inaccessible.
 
I remember my dad ripping our washing machine out and throwing it through the back door when I was a kid. It was on fire at the time. I wonder if he managed to isolate it first. I just remember being in awe of his seemingly super human strength!
 
My Mum used to do that every Saturday, when she did the weekly wash (cutting edge technology then, tin bath before). She'd manhandle the thing from the shed into the kitchen. The thing was louder than Concorde taking off.
bdc0925d5e593187956dd997933d6523.jpg
 
Ah the 'Toploader' - preferred the noise the band made than those clacking away. My mum used a pair of wooden tongs, metal sprung end that were so old that the wood was like velvet in texture (they saw some action) - a phenomenon as a child.
 
Ah the 'Toploader' - preferred the noise the band made than those clacking away. My mum used a pair of wooden tongs, metal sprung end that were so old that the wood was like velvet in texture (they saw some action) - a phenomenon as a child.
That has taken me back, my ma had tongs just the same they were always slippery and sleek on the wood.
 
Yep and there was a little plastic perforated lid, to cover the wet clothes as they were spun dried, with the metal lid closed.

As it's Xmas, I can also remember my Mum using metal quadruple stove steamers, to cook the veg & Xmas pudding.
 
Yep and there was a little plastic perforated lid, to cover the wet clothes as they were spun dried, with the metal lid closed.

As it's Xmas, I can also remember my Mum using metal quadruple stove steamers, to cook the veg & Xmas pudding.
My mum's was a perforated rubber disc, those were the days.
 
I use triple steamers, sometimes leave one empty which totally confuses me - doesn't take much!
 
That has taken me back, my ma had tongs just the same they were always slippery and sleek on the wood.
That's the ones - kind of entrancing as a child - she would use the same ones for boiling my dads snotty hankies so I wasn't always enamoured with them!
 
That's them - never got hit though - that's where the green garden cane came into it, an arms length plus 3 feet of cane she was still swift on her feet. I do love her, in her 89th year now we laugh about it!
 

Reply to Utility Room Sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
801
Hi everyone, I have recently had an extension built with a new Utility room. The electrician has put the sockets for the washing machine and...
Replies
22
Views
5K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
580
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
943

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock