R4BOE

hi

what code do you think should be atributed to a 2 core SWA cable used as part of a Main bonding conductor the steel Csa equivelent required is 64mm sq and the current 2 core 25mm sq swa is a BS 6346 with a steel csa of 60mm sq

the above info on the required CSA is from the ESC technial manual

the installatrion is mid - late 1980's TNS copper equivelent required is 10mm sq
 
Last edited by a moderator:
hi

what code do you think should be atributed to a 2 core SWA cable used as part of a Main bonding conductor the steel Csa equivelent required is 64mm sq and the current 2 core 25mm sq swa is a BS 6346 with a steel csa of 60mm sq

the above info on the required CSA is from the ESC technial manual

the installatrion is mid - late 1980's TNS copper equivelent required is 10mm sq

Whats it bonded to?

Sent from my GT-I9100 using Tapatalk
 
So straight from the armouring is a fly lead of some sort? What size is this? Have you.done an r2 test to see if your getting 0.05? Im swaying towards a C3.

Sent from my GT-I9100 using Tapatalk
 
If this is for a EICR I would be looking at what size earthing conductor is needed for the premises by use of the adiabatic I would then only code it if the main bonding conductor was under sized as with it being TNS you might find that what is installed is sufficient IMO !
 

Reply to what code for a under sized armouring as a main bonding conductor in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
710
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
527
EICR recently done, Swa sub mains armouring used for cpc & MEBPC. Installed 40 years ago, water/gas/structural bonding required, these are @ 10mm...
Replies
31
Views
4K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock