Sorry if this is a stupid question. Does the AC from the inverter connect to the load side of the meter or the supply side? I assume to measure the output of the panels it connects to the load side??

Apologies if this has been answered before/ stupid question

Regards

Erf
 
thanks

yes the generation meter. For some reason couldnt get my head around it!

So to clear it up, the output from the inverter i.e. the output from the panels connects into the supply side nof the generation meter then the load connection into the dedicated mcb in the consumer unit?

Thanks
 
Pretty much , not forgetting your appropriate isolation of course .

I am sorry to cut in on this are you certain that the inverter feeds the supply side and not the load , im sure ive read somewhere that the pv is always classed as load . any experts please clarify possibly with line diagram . Cheers
 
Jeff, the meter is there to measure the output of the inverter so the inverter has to be connected to the supply side. From left to right: inverter line, inverter neutral, neutral to consumer unit, line to consumer unit.
 
Definitely the correct information given here.

I know this as ours was wired up the wrong way round!!!

I contacted the installers after the 1st day when the meter reading hadn't changed and he suggested this would explain it. They came out straight away and corrected it but were amazed that their electrician had got it wrong as he's done many for them previously.

I guess it's just second nature for an electrician to think of the consumer unit as the supply side.
 

Reply to which way around for the generation meter??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
834
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock