hello guys been called to a house today, Large old place with 3phase supply.
Phases into 100ma rcd then split to feed duel rcd wylex boards on each floor.The home owners have had trouble with the 100ma s type tripping but not any of the 30ma in the consumer units,i was thinking it may be a fault with a neighbouring property feeding back up the stake (TT system)

Any ideas on way forward,we need the 100 to protect the sub mains.

Cheers all
 
If this is a big property with scores of circuits, it could well be an accumulation of leakage current. Don't forget that it's very possible that none of the individual 30mA RCD devices are seeing 30mA, the 100mA will be seeing the overall leakage current. Then of course, there is always the probability of 100Ma S type device being faulty. The only way your going to really confirm or otherwise is to test with a leakage current clamp meter. Ramp testing will at best give you an idea, as they tend to ramp in multiples of test mA, sometimes in multiples of 5mA, depending on what range they are set on. You may well have to increase that front end device to a 300mA S type, ...only by careful testing will let you know that!!
 
What make is the 100ma RCD? Recall a make from others that gave them plenty of bother, Control Gear IIRC
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
100ma stype tripping
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
ohlins,
Last reply from
D80,
Replies
5
Views
1,377

Advert