Correct - or not so!

I'd have installed metal switched fuses at 80A to enclose SWA conductors and offer protection.

How would you code?
This is a rudimentary issue and how I would Code it is not important. How are you assessing circuit protection for a distribution circuit is provided considering you do not know the characteristics of the protective device and whether this device is recommended for circuit protection of the consumers supply.
 
Main earth uses gas supply
Sorry bit confused with that. Looks like the main earth is coming from the cut out? And the SWA are you absolutely sure it is 16mm and not 10mm? I know it is difficult sometimes to assess cable size especially through a piccy. I agree I would have fitted a couple of maybe Lewden fused isolators maybe 63a cartridge fuses apart from a lack of room and location.
 
A ze of 0.14 ohms will ‘blow’ the fuse whether it be rated at 60,80 or 100 amp bs1361 or bs 88.
I find it harsh to say a C2 as the fuse would blow in less than 5 seconds on a TN system.
However you are only allowed to rely upon the distributors fuse where they allow that it can afford protection to the part of the installation between the origin and the main distribution point where overload and fault protection is provided at your DB.
So if they only allow 3 meters then you need to code accordingly in my opinion.

As for 16 mm on a 100amp fuse.
My opinion is that is the demand of the installation at time of inspection reveals that overload isn’t likely then I’d assess it on that basis.
If the demand was to change in the future then before any alterations in the future by an electrician, they would need to assess the existing demand and decide if it is acceptable to determine if the proposed alterations comply Which is what’s always required anyway.
 
Last edited:
Providing it is 16mmSQ as in the pics it looks like 10. 16mmSQ armoured Is good at 35m clipped direct for 100a. And providing the ZsDB is ok which you have proven there is not code relevent.
However I Disagree with only basic insulation in the meter enclosure, as meter readers have access and as such aren't competent. I'd C2 it on this count under section 526.

Could of staggered the isolators in the box, glanded the inner sheath to a small enclosure box flush with the bottom of the isolator with the top cut out.
 
Sorry bit confused with that. Looks like the main earth is coming from the cut out? And the SWA are you absolutely sure it is 16mm and not 10mm? I know it is difficult sometimes to assess cable size especially through a piccy. I agree I would have fitted a couple of maybe Lewden fused isolators maybe 63a cartridge fuses apart from a lack of room and location.
If i recall correctly the dno around here get right funny if you install something in the meter / cutout cabinet. I fitted a switched fuse for a cu change as the customer wanted it moved somewhere out of sight and they went right off on one when they came to pull the fuse so i coudl fit it in and do the change.... telling me we arent allowed to put stuff in the cabinet. its different if its indoors on a wall then its a free for all.
 

Reply to 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello everyone, I have recently qualified, though yet to start practising, as an electrician. I have noticed, at my home, the tails from the...
Replies
20
Views
11K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)
Hi All, I have my ELECSA assessment in a few weeks time. I was going to install an in-line water heater at a friends house but am now considering...
Replies
73
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock